Why aren't earth rods required on a TN-C-S or TN-S supply? In the US earth rods are mandatory for both. Two earth rods if the first one is over 25 ohms.
Here is how its typically done:
View: https://youtu.be/4vxYXzNtE9A?t=3459
#6 copper (13.3mm2) is run from the neutral bar of the first disconnect after the meter socket, down in conduit and connected to earth rods at least 6 feet apart. In this case he also bonds the conduit coming from the meter. Service looks to be 225amps in what is probably 4/0 (107.2mm2) copper.