Testing an installation - RCD's not testing properly (can get a good test occasionally.?)- Newish Megger recently calibrated
just tested RCD's at home and all good
All MCB's off, RCD's off, main switch off and main fuse removed, no alternative supplies
can get a good tingle off of the earth - disconnected earth bonding to water (no gas or oil etc) and main earth bond no voltage on consumer unit earth bar measured
PME installation - overhead supply - old uninsulated neutral style (N-L 243v , L-E 243v)
ALL circuits test perfectly IR, R1R2, ZE, ZS etc (supply 0.16 ohm Ze same as main bond approx 450mm long)
Can get a goodly spark to the earth bar in the consumer unit from either.... - have a video of this - showing exactly above
cannot measure a voltage across either and earth in the consumer unit common but they spark
Realise there will be earth potential on water pipework etc
Any ideas ?
just tested RCD's at home and all good
All MCB's off, RCD's off, main switch off and main fuse removed, no alternative supplies
can get a good tingle off of the earth - disconnected earth bonding to water (no gas or oil etc) and main earth bond no voltage on consumer unit earth bar measured
PME installation - overhead supply - old uninsulated neutral style (N-L 243v , L-E 243v)
ALL circuits test perfectly IR, R1R2, ZE, ZS etc (supply 0.16 ohm Ze same as main bond approx 450mm long)
Can get a goodly spark to the earth bar in the consumer unit from either.... - have a video of this - showing exactly above
cannot measure a voltage across either and earth in the consumer unit common but they spark
Realise there will be earth potential on water pipework etc
Any ideas ?