Testing an installation - RCD's not testing properly (can get a good test occasionally.?)- Newish Megger recently calibrated
just tested RCD's at home and all good

All MCB's off, RCD's off, main switch off and main fuse removed, no alternative supplies

can get a good tingle off of the earth - disconnected earth bonding to water (no gas or oil etc) and main earth bond no voltage on consumer unit earth bar measured

PME installation - overhead supply - old uninsulated neutral style (N-L 243v , L-E 243v)

ALL circuits test perfectly IR, R1R2, ZE, ZS etc (supply 0.16 ohm Ze same as main bond approx 450mm long)

Can get a goodly spark to the earth bar in the consumer unit from either.... - have a video of this - showing exactly above
cannot measure a voltage across either and earth in the consumer unit common but they spark

Realise there will be earth potential on water pipework etc

Any ideas ?
 
It sounds like the circulating currents that are common in PME, with some current from other installations returning to the transformer via your bonding and the earthed services. It's not necessarily a problem, seeing as you are not getting a significant voltage discrepancy or high Ze that would indicate a broken PEN. It might be an indication of why PME specifies a larger minimum size of MEB conductor, and why the gas meter people put a cable across the meter pipework before removing or fitting a meter, to avoid exactly that spark.

I don't think it is necessarily related to the RCD behaviour.
 
It sounds like the circulating currents that are common in PME, with some current from other installations returning to the transformer via your bonding and the earthed services. It's not necessarily a problem, seeing as you are not getting a significant voltage discrepancy or high Ze that would indicate a broken PEN. It might be an indication of why PME specifies a larger minimum size of MEB conductor, and why the gas meter people put a cable across the meter pipework before removing or fitting a meter, to avoid exactly that spark.

I don't think it is necessarily related to the RCD behaviour.
Hi
Thanks for that
Surely any circulating currents would effect the rcd operation - I can get a good test on both rcd's sporadically -was there almost three hours and tested rcd's randomly many times over that period - 50% success , often two or three tests on the trot good..
Surely this cannot be acceptable ?
Would the DNO be able to check / sort ?
Thanks
 
Surely any circulating currents would effect the rcd operation -
No, as the RCD measures the imbalance between L & N, is it not looking at any CPC current that might be circulating (assuming it is an RCD and not an ancient VOELCB).

Now if you have an N-E fault it could be a different situation, as you might have some anti-phase current in the N making the trip threshold for the RCD test higher than usual, etc. But you should always (and apparently already have) have checked the global IR (overall L+N to E) situation first before wondering about potential RCD issues.
 
No, as the RCD measures the imbalance between L & N, is it not looking at any CPC current that might be circulating (assuming it is an RCD and not an ancient VOELCB).

Now if you have an N-E fault it could be a different situation, as you might have some anti-phase current in the N making the trip threshold for the RCD test higher than usual, etc. But you should always (and apparently already have) have checked the global IR (overall L+N to E) situation first before wondering about potential RCD issues.
Surely if you have circulating currents on a pme system when a second earth via water pipes etc is introduced this would affect the rcd ?
 

Reply to Earth Sparkin (not ur usual......) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top