I have always used 1.5mm single earth when wiring sockets in a conduit system, a guy on site just now is saying it should be 2.5mm earth same as live amd neutral conductors, is this correct amd why would it change because u use conduit ??
 
If you read the regs the cpc should be a minimum of half the size of the phase conductor,ie a 1.5 earth on a 2.5 phase conductor,however I must admit having spent most of my life in industry we always used 2.5 for all three.
 
The minimum CSA for a protective conductor that is not incorporated in a cable such as T&E is 2.5mm², if provided with mechanical protection, 4mm² if not provided with mechanical protection.
Regulation 543.1.1 ...
"If the protective conductor:
(iii) is not an integral part of a cable, or
(iv) is not formed by conduit, ducting or trunking, or
(v) is not contained in an enclosure formed by a wiring system,
the cross-sectional area shall not be less than 2.5mm² copper equivalent if protection against mechanical damage is provided, and 4mm² copper equivalent if mechanical protetion is not provided (see also Regulation 543.3.1)."

Not 100% sure what exactly an enclosure formed by a wiring system is?
 
I can't see it meaning containment.
Containment would provide mechanical protection, and if mechanical protection is provided the minimum CSA is 2.5mm².
Parts (iii) - (v) allow the protective conductor to be smaller than 2.5mm².
 
true. another ambiguous reg. you could argue that sheathed singles are mechanically protected as opposed to normal single insulated singles. it's open to more than one interpretation.
 
because the regs say: "The minimum CSA for a protective conductor that is not incorporated in a cable such as T&E is 2.5mm²"

I presume the reason being that when incorporated in T&E the CPC is somewhat protected by being surrounded by the other conductors and the sheathing, whereas in singles in an enclosure all conductors have equal protection.
 
true. another ambiguous reg. you could argue that sheathed singles are mechanically protected as opposed to normal single insulated singles. it's open to more than one interpretation.
Very ambiguous.
I'm wondering whether it's a reference to busbar trunking?
The definition for a wiring system states: "An assembly made up of cable or busbars and parts which secure and, if necessary, enclose the cables or busbars."
 
because the regs say: "The minimum CSA for a protective conductor that is not incorporated in a cable such as T&E is 2.5mm²"

I presume the reason being that when incorporated in T&E the CPC is somewhat protected by being surrounded by the other conductors and the sheathing, whereas in singles in an enclosure all conductors have equal protection.

Regs smegs
 

Reply to earth wire sizing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top