R

roukel01

Morning Folks.

Doing some work at a customers house and they've bought one of these Metal Sheds from B&Q. He wants power to it. The plan is to run a 4mm SWA to it for a socket and lighting. With the shed being metal, I'm going to earth it, however, should it be a 10mm earth back to the board, or can I get away with earthing it via the swa?

Many Thanks.
 
Watch what fittings you put in the shed, even though they keep the rain out, they sweat more than a fat plumber and get full of condensation.
 
Watch what fittings you put in the shed, even though they keep the rain out, they sweat more than a fat plumber and get full of condensation.

Haha, yeah we noticed the condensation. Everything installed is weatherproof!
Went to have a look this morning, there are Icicles hanging from the roof!
 
Though i hate to bring it up, is your house supply PME/TNC-S?? I'd also check if the steel shed is earthy in it's own right too (depends if it has a concrete base that the sheds been bolted too)!! So maybe an IR test to see if it's over 23K ohms or under !! If the answer to both is Yes, ...then you'll need that 10mm bonding connection....
 
That's a paper written by John Peckham, very useful
It shows which SWA cables can be used with the armour as a CPC.
Unfortunately, it does not show any SWA cables where the armour can be used as a bonding conductor.
 
That's a paper written by John Peckham, very useful
It shows which SWA cables can be used with the armour as a CPC.
Unfortunately, it does not show any SWA cables where the armour can be used as a bonding conductor.

I am obviously missing something. This guide does say
3. If the SWA is used as a main equipotential conductor other than on a PME system it must have a copper equivalent CSA, for CSAs over 25mm, of not less than half the cross sectional area of the associated earthing conductor and not less than
6mm2 to comply with 544.1.1. If the installation is PME then the copper equivalent CSA of the SWA must comply with table 54.8.

Apart from the typo (I assume ", for CSAs over 25mm, " should read "under 25mm") that implies that the swa can be used for bonding. Any SWA normally used in domestic has a copper equivelant CSA of >10mm2.
What am I missing?
 
No the ratio of conductivity between copper an steel is about 8:1.
Copper is eight times more conductive than steel.
As such for the SWA to have copper equivelance, the CSA of the armour would have to be in the region of 80mm².
With 2core 70° C PVC cable the minimum CSA of the conductors would be 70mm², 3core, 50mm², 4core, 25mm².
Of course, if you are using conductors with those CSAs, the chances are that you would require a larger than 10mm² bonding conductor.
 

Reply to Earthing a metal shed in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

Twin and earth on its own isnt going to meet the requirements for burial. Why not use Swa ?
Replies
1
Views
287
I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
Replies
7
Views
671

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top