Earthing and bonding sizing | on ElectriciansForums

Discuss Earthing and bonding sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

J

JulianC

Righty, I may be suffering from brain fade on this so please bear with me....

In a domestic situation up to 100A it is generally accepted that for a TN-C-S supply, earthing and bonding must be 16mm & 10mm respectively and if this is not present, we must upgrade it.

The 10mm bonding is plain to see from reg 544.1.1 where it is categorically stated in table 54.8.
But where does it say that if you have a PME supply the main earth must be 16mm? From 543.1.1 we know that the earth conductor size can either be selected from table 54.7 (where 16mm is indeed the minimum) or it can be calculated from the adiabatic equation. Why then, providing the results of the adiabatic equation say so, can we not have a PME supply with 10mm for both earthing and bonding? Or can we and I've just not been paying attention?

General consensus seems to be that for T-T or TN-S we can calculate and perhaps get away with 10mm earth and 6mm bonding but every time TN-C-S is mentioned we for some reason need a 16mm earth & 10mm bonding. Why not 10mm for both if the adiabatic says it's OK?

Ta.
 
Last edited by a moderator:
I dont do equations. But what i do do is, belt and braces just to make sure. I bond main earth 16mm, main equipotential at 10mm, and owt else gets 6mm, irrespective of TT, TNS, TNCS

The reasons behind this are several. The wholesaler stocks it, i keep less reels of cable in the van, it is adequate for all the current earthing arrangements i come across, and last but not least i dont have to do sums. Oh nearly forgot, the BRB says I can.

Cheers..........Howard
 
I dont do equations. But what i do do is, belt and braces just to make sure. I bond main earth 16mm, main equipotential at 10mm, and owt else gets 6mm, irrespective of TT, TNS, TNCS

The reasons behind this are several. The wholesaler stocks it, i keep less reels of cable in the van, it is adequate for all the current earthing arrangements i come across, and last but not least i dont have to do sums. Oh nearly forgot, the BRB says I can.

Cheers..........Howard

my type of logic :)
 
it can be used for sizing cpc/ earth, but not for bonding
hi mate for a tn-s system 100amp, 25mm tails, Ze 0.26ohm
to do the adibiatic equation for earthing conductor is it the voltage divided by the Ze to get the fault current then I squared x time then square root and finaly divide by K could you please explain if this is right cheers
 

Reply to Earthing and bonding sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
669
loz2754
L
Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top