I was replacing a socket that had a cracked face and as I took said socket off I noticed the armour was earthed by using BS951 clamps. I wasn’t expecting to see any earthing of the armour as the SWA was in a conduit drop to the socket.

I’ve never seen it done like that before but now I walk around the factory and automatically assume every SWA I see entering a conduit drop will have the armour earthed with the clamps. Never been referenced on any EICRs we’ve had done in the past.

I don’t like it as the SWA hasn’t been glanded, just been shoved down the conduit.

I took the conduit drops away and glanded the SWA appropriately with the use of Earth Nuts.

Is the use of BS951 clamps acceptable practice for the earthing of armour?

[ElectriciansForums.net] Earthing Armour with BS951 clamps?
 
Certainly not good practice, and I’m surprised whoever did this didn’t think the earth terminal in the bottom right of a plastic box needed earthed too.

I have found a couple of those BG sockets with an earthed plastic box in the factory!

Luckily it's only one area that has the SWA dropped in conduit so I think I'll be amending those.

Cheers littlespark.
 
I was replacing a socket that had a cracked face and as I took said socket off I noticed the armour was earthed by using BS951 clamps. I wasn’t expecting to see any earthing of the armour as the SWA was in a conduit drop to the socket.

I’ve never seen it done like that before but now I walk around the factory and automatically assume every SWA I see entering a conduit drop will have the armour earthed with the clamps. Never been referenced on any EICRs we’ve had done in the past.

I don’t like it as the SWA hasn’t been glanded, just been shoved down the conduit.

I took the conduit drops away and glanded the SWA appropriately with the use of Earth Nuts.

Is the use of BS951 clamps acceptable practice for the earthing of armour?

View attachment 117685
BS 951 states that clamps to this standard are not intended for connection to the armour or sheath of a cable and requires the packaging of the clamp to include the warning “Not intended for use on the sheath or armour of a cable
 

Reply to Earthing Armour with BS951 clamps? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
910
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
643
loz2754