I've been doing a lot of research, and am hearing a lot of conflicting information on this subject. Currently working on an important job and want to get this perfect, and the time is coming soon to connect the new consumer unit up to the supply, so would be interested to get some more feedback here.
So to put it in hypothetical terms, lets say you had a 100 amp TN-S supply & meter located on the outside of the house, and the consumer unit were to be relocated in a room within in the house, 5 - 10 m away from the supply, with the cable disappearing underground. How would you do it in the most efficient and compliant way possible?
Here's what I'm thinking I'd do:
Install 100 amp metal clad switched fuse next to meter. Meter tails go into this. To get from here to the new CCU I'd use 2 core 25mm SWA, glanded and Earth nutted to switched fuse enclosure, with a 16mm copper flying lead connecting Earth nut to MET. The same same gland / Earth nut arrangement would apply at the CCU, connecting the Earthing bar to SWA armour. So no unsightly additional CPC tagging along with the SWA, and no unnecessary re purposing of a core of 3 core SWA.
Assuming disconnection times / adiabatic equations etc. all work out (which so far given optimal circumstances seem that they do), can anyone see any problems with this arrangement, or is there a better way? Also - on the schedule of results, if using this arrangement, what would the e̶a̶r̶t̶h̶i̶n̶g̶ ̶c̶o̶n̶d̶u̶c̶t̶o̶r̶ CPC of the distribution circuit (thanks for clarification of terms there davesparks) material be listed as, given that it's a combination of copper and steel?
Generally interested to hear how you'd do it / have done it, and reasons why. I am inexperienced but very keen to really get to grips with best practice & the theory behind it.
EZ
So to put it in hypothetical terms, lets say you had a 100 amp TN-S supply & meter located on the outside of the house, and the consumer unit were to be relocated in a room within in the house, 5 - 10 m away from the supply, with the cable disappearing underground. How would you do it in the most efficient and compliant way possible?
Here's what I'm thinking I'd do:
Install 100 amp metal clad switched fuse next to meter. Meter tails go into this. To get from here to the new CCU I'd use 2 core 25mm SWA, glanded and Earth nutted to switched fuse enclosure, with a 16mm copper flying lead connecting Earth nut to MET. The same same gland / Earth nut arrangement would apply at the CCU, connecting the Earthing bar to SWA armour. So no unsightly additional CPC tagging along with the SWA, and no unnecessary re purposing of a core of 3 core SWA.
Assuming disconnection times / adiabatic equations etc. all work out (which so far given optimal circumstances seem that they do), can anyone see any problems with this arrangement, or is there a better way? Also - on the schedule of results, if using this arrangement, what would the e̶a̶r̶t̶h̶i̶n̶g̶ ̶c̶o̶n̶d̶u̶c̶t̶o̶r̶ CPC of the distribution circuit (thanks for clarification of terms there davesparks) material be listed as, given that it's a combination of copper and steel?
Generally interested to hear how you'd do it / have done it, and reasons why. I am inexperienced but very keen to really get to grips with best practice & the theory behind it.
EZ