Earthing arrangement | on ElectriciansForums
Discuss Earthing arrangement in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
BLBelfast
A thing that has made me doubt what ive always done. When testing various domestic premises I have been doing a PEFC test and a PSCC test to determine if the installation is TN-S OR TN-C-S.
I was always told this is fine as the ka value will be the exact same on a TN-C-S. However today I got a Value of Pefc 617 and PSCC 586. That would make me think it was TN- S but I highly suspect this premises was TNCS. Is their an allowance for that much of a difference when testing to find out the earthing arrangement. Got a Zdb of .4 and a Ze of .21
Any help appreciated
Sent from my SM-G920F using Tapatalk
if it's PME then the N and E are shorted at the cut-out, so the pefc and pssc will be the same.if not, it;s not PME. or there could be a bit of hogh resistance on the N-E connection, as your figures are fairly close.
Yeah I'm 99% sure it's a TNCS system. Never thought about the high resistance in the N and E link. The cable is small enough that it looks to be TNCS aswell. I was always taught to test or ring the DNO. You can't always tell by simply looking.
The Ze alone suggests TN-C-S.
The difference between the Ze and Zdb though, does suggest a high resistance somewhere.
How long are the meter tails?
For a do,estimated supply I does seem to suggest that, but could equally be a sign that the DNO has been in the area bodging old lead distribution and service cables with randomly installed N-E connections all over the place.
Concur with davesparks. I recently asked the DNO about converting a TN-S system to TNC-S, mainly cos the installation had an earth rod as well and I wonder if the lead sheath was unstable or something. DNO came and had a look, and said to convert to a TNC-S myself. He said the lead sheathed supply cable was probably connected to a new PME supply somewhere out in the road anyway!
Reply to Earthing arrangement in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
    • Friendly
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.