B

bks

Why it would be better off Changing tns to tt and comply with reg. because of not having reliable earth. When installation was tns earthing with Ze 18 ohms because swa was used as earth is corroded and 22ohms after changed to tt. Intallation is rcd protected before and now. Can anyone help me to understand about this principle change tns to tt. Except spending fortune to replace that swa to 3 core to keep tns. Client doesn't want to spend more.
 
Why it would be better off Changing tns to tt and comply with reg. because of not having reliable earth. When installation was tns earthing with Ze 18 ohms because swa was used as earth is corroded and 22ohms after changed to tt. Intallation is rcd protected before and now. Can anyone help me to understand about this principle change tns to tt. Except spending fortune to replace that swa to 3 core to keep tns. Client doesn't want to spend more.

If the earth is unreliable thats a risk, if the 0.18 is not guaranteed and wanders you cannot rely on it.
As long as you get down to an acceptable level of Ze on your earthing rods this should be a reliable earthing system.
The reading may well change from summer to winter on your earth fault path so be aware as to the time of year that you are installing it, so if you are on the high side and the ground is as wet as its going to get then during a dryer season the Ze reading may well go higher and become unstable.
I dont do much in the way of TT systems but I think the maximum reading should be 200 ohms but really you should be looking to get substantially lower than that.
There is a certain person on here that will give you a whole lot more info on earth stakes etc but I'll mention no names.
Check with others on the maximum limits of a TT system
 
It sounds like you've already done a TT conversion. As Dilb says the earth on a TNS would have been the DNO's responsibility to provide remedy but if you've converted it I'm not sure where you stand plus the DNO's distribution network records would now be incorrect.
 
Thanks folks for your reply but this problem I am having in the caravan park which is from one of the DU to the chalet, not from the supply origin which is DNO 's responsibility.
I just want to know what reason changing tns to tt would be better off if the installation has high earth even installation is already rcd protected and without replacing cable.
 
So the most important question is "where is the swa running from and to?"

EDIT: So you as the park owner has this issue. How long is the run to the chalet?
 
Last edited by a moderator:
If,as you have said,the unreliable earth reading is due to a corroded armouring,then THATS your immediate problem. Now can i have the first week in August for free? :tounge_smile:
 
The SWA has corroded because the cable wasn't laid correctly in the first place. The sheath of the cable has been compromised, probably due to cable being laid in the trench, with the presence of sharp stones/debri and being backfilled with the excavated soil that is also laden with sharp stones, etc!!

You now have 3 choices, 1) replace the SWA cable, 2) install a suitably sized separate CPC, 3) TT the cabins installation. The 3rd choice would be my last choice, unless you are prepared to put a concerned effort into getting a lower single figure Ra value....
 
still i didn,t get the answer what i am looking for


What exactly are you looking for then??

You were asked where the cable is running from and to?? Is it from an adjacent hook-up unit to the chalet or from a central distribution DB to the adjacent hook-up unit, where the SWA has corroded away??
 

Reply to earthing arrangement in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top