1, lightning grounding can be completely used in the building foundation of the steel as the grounding body, but must be the steel bar electrical through welding together, and use the vertical steel bar in the building column as the lead wire, has been connected with the roof lightning protection facilities.
2, a lot of requirements to lead out the steel bar is used to do artificial grounding, that is in the use of the building foundation itself to do grounding can not meet the requirements of the resistance, and even if the artificial grounding, the effect is much worse than the building itself to do grounding body.
Notes:
1. Conduct good electrical connection of the foundation reinforcement, at least ensure that the outer ring is connected. It is recommended to use 12MM round steel for the bonding material, and the welding length is about 150MM.
2, lead off the average distance should be less than 25 meters, if the house is not large, four corners of a lead off the line is good.
3. It is recommended to use 2 16MM rebar or 4 14MM rebar for each lead wire. Make sure that the lead wire connects the grounding body to the roof lightning arrester.