looking thru my regs now for curves but cant find BS88 HRC on the list
The PSSC on 3 Phase will be higher than the PFC so you can't be wrong if using the figure if that's all you have to go on ? or am I wrong in thinking that ?
I think things are getting a bit bogged down with half explanations.
When determining the minimum CSA of an earthing conductor for a 3 phase installation, you would measure the PEFC for each phase, then use the highest measured value in your calculations.
Where PME conditions apply, the minimum CSA should be determined from the appropriate table in BS7671, based on the CSA of the line conductors.
Where (as appears to be the case in this instance) an EICR is being conducted, it usual to first ensure by calculation that the CSA is adequate for fault protection, then to examine the conductors for signs of over heating.
If the CSA is adequate for fault protection, but is undersized as per the table in BS7671, it generally accepted that no upgrading is required, as long as there are no signs of heat damage to the earthing/bonding conductors.
BS88 fuses are HRC.
Agreed.
Things are also getting bogged down however with people chipping in with "Double your PFC to get the true PFC" when we are talking about sizing earthing conductors. I think it's also getting bogged down with people who don't quite know the difference between PEFC and PSSC.
Back to basics is a suggestion I'd be inclined to make!
Who said double your PSSC to get the true PFC ?
I think one of the original posts says it all, I am taking data from a PIR or EICR which might as well be treated as bog paper......
I will go back and do some looking and testing myself next week. however.......... is the original calc ok assuming I alter 't' ???
Just re-read the op and realise I've been quoting pssc when it says clearly says pfc. Gods knows what I'm on.
I think one of the original posts says it all, I am taking data from a PIR or EICR which might as well be treated as bog paper......
I will go back and do some looking and testing myself next week. however.......... is the original calc ok assuming I alter 't' ???