I think things are getting a bit bogged down with half explanations.
When determining the minimum CSA of an earthing conductor for a 3 phase installation, you would measure the PEFC for each phase, then use the highest measured value in your calculations.
Where PME conditions apply, the minimum CSA should be determined from the appropriate table in BS7671, based on the CSA of the line conductors.
Where (as appears to be the case in this instance) an EICR is being conducted, it usual to first ensure by calculation that the CSA is adequate for fault protection, then to examine the conductors for signs of over heating.
If the CSA is adequate for fault protection, but is undersized as per the table in BS7671, it generally accepted that no upgrading is required, as long as there are no signs of heat damage to the earthing/bonding conductors.

BS88 fuses are HRC.
 
I think things are getting a bit bogged down with half explanations.
When determining the minimum CSA of an earthing conductor for a 3 phase installation, you would measure the PEFC for each phase, then use the highest measured value in your calculations.
Where PME conditions apply, the minimum CSA should be determined from the appropriate table in BS7671, based on the CSA of the line conductors.
Where (as appears to be the case in this instance) an EICR is being conducted, it usual to first ensure by calculation that the CSA is adequate for fault protection, then to examine the conductors for signs of over heating.
If the CSA is adequate for fault protection, but is undersized as per the table in BS7671, it generally accepted that no upgrading is required, as long as there are no signs of heat damage to the earthing/bonding conductors.

BS88 fuses are HRC.

Agreed.

Things are also getting bogged down however with people chipping in with "Double your PFC to get the true PFC" when we are talking about sizing earthing conductors. I think it's also getting bogged down with people who don't quite know the difference between PEFC and PSSC.

Back to basics is a suggestion I'd be inclined to make!
 
Agreed.

Things are also getting bogged down however with people chipping in with "Double your PFC to get the true PFC" when we are talking about sizing earthing conductors. I think it's also getting bogged down with people who don't quite know the difference between PEFC and PSSC.

Back to basics is a suggestion I'd be inclined to make!

Who said double your PSSC to get the true PFC ?
 
I think one of the original posts says it all, I am taking data from a PIR or EICR which might as well be treated as bog paper......

I will go back and do some looking and testing myself next week. however.......... is the original calc ok assuming I alter 't' ???
 
I think one of the original posts says it all, I am taking data from a PIR or EICR which might as well be treated as bog paper......

I will go back and do some looking and testing myself next week. however.......... is the original calc ok assuming I alter 't' ???

And as long as you use the correct value for 'I', which is the prospective earth fault current, the highest measured value between one of the line conductors and earth.
 
I have a feeling that you are going to be right on the edge of the 5s disconnection time with that PFC and rating of fuse. If the PEFC is any lower, you may have trouble satisfying the 5s disconnection time.
 
I think one of the original posts says it all, I am taking data from a PIR or EICR which might as well be treated as bog paper......

I will go back and do some looking and testing myself next week. however.......... is the original calc ok assuming I alter 't' ???

Don't worry too much about the DNO fuses, they are basically no concern of your's, the DNO use their own parameters for the protection of their network distribution cables. Any protection that is on the consumers side of this installation will be based on the manufacturers OCPD minimum ''Zs'' requirements, not the Ze value, although the Ze value at the source will play a significant part of the installations Zs/Zdb values...


So when you go back to do your'e own tests, check both Ze and Zs....
 

Reply to Earthing...... Cable size any help appreciated in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
731
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

  • Question
Thanks for the advice! Much appreciated
Replies
6
Views
912
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top