Alright, so what do you think of these CPC sizes in relation to the phase conductors?


90*C insulation, TN-C-S supply


MCB / Live / CPC / Multiplier

15 - 2.08mm2 - 2.08mm2 - X 1

20 - 3.31mm2 - 3.31mm2 - X 1

60 - 13.30mm2 - 5.261mm2 - X 0.3955

100 - 26.67mm2 - 8.367mm2 - X 0.3137

200 - 85.01mm2 - 13.30mm2 - X 0.1564

300 - 177mm2 - 21.15mm2 - X 0.1195

400 - 304mm2 - 26.67mm2 - X 0.0877

500 - 456mm2 - 33.62mm2 - X 0.0737

600 - 760mm2 - 42.41mm2 - X 0.0558


0.3, 0.1 and 0.05 multiplier difference ever encountered in the UK?
 
Well, that would be an assumption...
It would just as we in the UK assume the tabulated values in BS 7671 have been calculated and vetted by others before going to print. We don't go out of our way to prove them wrong but might need to verify a conductor by use of adiabatic calc!
Not really sure what your point is, if non standard sizes seems meaningless!
 
It would just as we in the UK assume the tabulated values in BS 7671 have been calculated and vetted by others before going to print. We don't go out of our way to prove them wrong but might need to verify a conductor by use of adiabatic calc!
Not really sure what your point is, if non standard sizes seems meaningless!
@DefyG I've just googled the sizes and it seems they are the metric equivalent of AWG (American wire gauge) system so it seems they are standard American sizes. Every day's a school day!
 
It would just as we in the UK assume the tabulated values in BS 7671 have been calculated and vetted by others before going to print. We don't go out of our way to prove them wrong but might need to verify a conductor by use of adiabatic calc!
Not really sure what your point is, if non standard sizes seems meaningless!

These are standard sizes for North and South America.

The ratio between live and earth is huge, so much so my point revolves around the uncertainty that that the CPC will survive a fault.
 
Non standard to the UK so meaningless to me and I'm sure other UK electricians as I am not upto speed with the US regulations on conductor sizes or calculation using a US adiabatic formula!
Have you tried calculating yourself to prove the sizes are ok or not?
Need more information in any case.
Perhaps the US regulations do not allow for protection of the cable in the event of a fault?
 
Non standard to the UK so meaningless to me and I'm sure other UK electricians as I am not upto speed with the US regulations on conductor sizes or calculation using a US adiabatic formula!
Have you tried calculating yourself to prove the sizes are ok or not?
Need more information in any case.


Truth be I'm not sure how to go about calculating them as there is nothing explicit in the NEC about it. Closest thing is the formula for tap conductors. Which I guess could work in theory.

Perhaps the US regulations do not allow for protection of the cable in the event of a fault?


That has gone through my mind, and thats what I'm trying to figure out to be honest.
 
[ElectriciansForums.net] Earthing Conductor Size- Good?



This applies to tap conductors, but nothing in regards to the CPC.
 
0.3, 0.1 and 0.05 multiplier difference ever encountered in the UK?
Not as "rule of thumb" design, typically ours is 0.5 or a few smaller ones in the case of T&E which are normally limited to the 6-50A region.

Those cable sizes are mostly OK provided your breaker operates fast (i.e. magnetic trip) and your PFC is moderated for the smaller sizes. Running adiabatic calculations for k=100 (typical copper 90C thermoplastic) I get:
MCB​
Live​
CPC​
Multiplier​
I2t limit​
15​
2.08​
2.08​
1​
4.33E+04​
20​
3.31​
3.31​
1​
1.10E+05​
60​
13.3​
5.261​
0.3955​
2.77E+05​
100​
26.67​
8.367​
0.3137​
7.00E+05​
200​
85.01​
13.3​
0.1564​
1.77E+06​
300​
177​
21.15​
0.1195​
4.47E+06​
400​
304​
26.67​
0.0877​
7.11E+06​
500​
456​
33.62​
0.0737​
1.13E+07​
600​
760​
42.41​
0.0558​
1.80E+07​

Looking at some let-through curves for Hager 100A-250A MCCB (just to hand) it is showing about 5E5 at 5kA PFC, and 4E6 at 40kA PFC. Hence short runs on a 40kA board for your CPC at 200A and below are at risk, even for a high but not unheard of "domestic" fault of 5kA, your 60A and below is at risk.

Of course, depending on the length and so on, it might be OK. But to me it is really marginal as if you have Zs and/or fault impedance that fails to hit the magnetic trip region then those MCCB let-through values are in the 6E6 to 6E7 region and a risk of burning them out even at the highest size in that table.
 

Reply to Earthing Conductor Size- Good? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top