It is just the I2t values scientific notation, sometime in lazy format. So:
500,000 = 5 * 10^5 = 5.0E+05 = 5E5
Yes, your worst-case is not always the highest fault.
Usually fuses decrease in I2t as you go from low overload / long disconnect to high current fast faults. There it is the longest time (highest Zs, etc) that is worst.
MCCB & MCB have two regions, the thermal one is quite slow so the 't' in I2t is large, and while the magnetic trip is fast at ~10ms in many cases, it does not get faster or limit the fault current to a great degree as PFC goes up. So typically your worst-case points in the breaker design is either max PFC, or just below the magnetic trip point where 't' is long but 'I' is fairly high.
I'm still confused as to what the I2t limit represents. Joules?
No magnetic trip sounds like an utter disaster for any usable protection. The thermal element is simply not fast enough (unlike a fuse, but its heating element is on a one-way trip to vapour).
I will go trip curve hunting- however- I think my eyes were just opened again... you might be right. As in spot on. But I'm still willing to challenge the concept. ?
Ok- here is a commercial/industrial US breaker trip curve:
If I'm reading the above time current curves correctly:
0.8 disconnection time on thermal takes about (roughly) 15x the handle rating worse care.
0.4 disconnection time on thermal takes about (roughly) 22x the handle rating worse case.
Assuming a 20 amp breaker-
15 x 20= 300 amps. At 120 volts a loop of 0.4 ohms is required.
22 x 20= 440 amps. At 277 volts a loop of 0.62 ohms is required.
A 500 foot circuit run consisting of 3.31mm2 wire has a R1+R2 of 2 ohms.
3.31mm2 wire has an 60Hz AC Resistance of 0.002 ohms per foot at 75*C.
At 120 volts I am limited to a 100 foot run. (30 meters)
At 277 volts I am limited 50 a 155 foot run. (47 meters)
Not unrealistic for a good chunk of circuits.
Technically I am incorrect to use 120 and 277 volts in that supplies vary below this value, but at the same time a 75*C resistance covers it reasonably well for the discussion at hand IMO.
Am I correct to conclude that it is indeed possible to provide adequate disconnection times with US breakers when the fault current does not trip the breaker magnetically? Or is this just me being overly wishful?
My mind keeps telling me that it is possible to achieve 0.8 and 0.4 with thermal elements. But I am humble in my argument. ?