Alright, so what do you think of these CPC sizes in relation to the phase conductors?


90*C insulation, TN-C-S supply


MCB / Live / CPC / Multiplier

15 - 2.08mm2 - 2.08mm2 - X 1

20 - 3.31mm2 - 3.31mm2 - X 1

60 - 13.30mm2 - 5.261mm2 - X 0.3955

100 - 26.67mm2 - 8.367mm2 - X 0.3137

200 - 85.01mm2 - 13.30mm2 - X 0.1564

300 - 177mm2 - 21.15mm2 - X 0.1195

400 - 304mm2 - 26.67mm2 - X 0.0877

500 - 456mm2 - 33.62mm2 - X 0.0737

600 - 760mm2 - 42.41mm2 - X 0.0558


0.3, 0.1 and 0.05 multiplier difference ever encountered in the UK?
 
If you paste these in to spreadsheet cells it should give you the k-values for copper, aluminium and iron/steel:

=226*SQRT(LN(1+(C6-C5)/(234.5+C5)))

=148*SQRT(LN(1+(C6-C5)/(228+C5)))

=78*SQRT(LN(1+(C6-C5)/(202+C5)))

Assuming your start temperature is located in cell C5 and your stop temperature in cell C6 (both deg C)
 
For example, typical PVC has start 70 and stop 160 (deg C) for the adiabatic change. The above equations (if set for 1 significant digit) should give you:
  • 115.0
  • 76.0
  • 41.7
For the k-values.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Earth

Thread Information

Title
Earthing Conductor Size- Good?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
42
Unsolved
--

Advert

Thread statistics

Created
Cookie,
Last reply from
Cookie,
Replies
42
Views
4,283

Advert

Back
Top