View the thread, titled "earthing conductors" which is posted in Australia on Electricians Forums.
S
sparks4
hello can anyone help me all i want to know is are 4mm main earth and main bonding conductors ok? as in passing a periodic inspection?
its a tns
external is 0.06 ohms
pfc is 2.9ka
talis are 25 mm
and it has an 30ma rcd main switch
i always asumed to minimum was 6mm but someone is questioning my snag on my report
many thanks:cyclist:
I've not got my BGB to hand but a rough calculation tells me that the mimimum required csa of the earthing conductor is around 8mm, so it should really be a 10mm cable in there. I assume the cutout fuse is a BS 88?
You don't tell us the supply.
However 4mm² will be fine as an earth conductor for 60A and 80A.
Code 4 for undersized bonding conductors.