Hi just after opinions on this one got three 3 phase supplies all 25mm 4 core swa, armour not been used for earth would you run a seperate 16mm earth for each supply or just loop all the earths from 1 16mm all the supplies are right next to each other
 
Why cant you use the armour?

You've got 3 cables all running to and from the same locations?
If they were all running to different places, i'd say 1 x 16mm each...
It doesn't seem enough... but then 3 sounds like too much.
Go for 2 x 16mm:rolleyes:
 
If you have correctly sized the main earth for the 3 phase supply to the main board, the surely you should use the same sizing formula for sizing the main earthing conductors to the remaining 3 sub main distribution boards, after all commonsense rules OK.
 
Hi - a 16mm for each and you probably don't need to look further, but otherwise few questions to help clarify -
Installation means of earthing?
Are sub boards having the same earthing design? Incoming conductor size?
Bonding requirements?
 

Reply to Earthing for 3 phase boards in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
712
Came across 3No 1ph heaters connected by 2xT&E cables from a 3phase supply on an installation whilst carrying out an EICR few years back...
Replies
9
Views
788

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top