Earthing for garage water service?

If a garage that has a 3-core 6mm[SUP]2[/SUP] SWA supplying the power to it & has a small bathroom in it, what size of earthing is required for the pipework for the water? In normal circumtances it's obviously a 10mm[SUP]2 [/SUP]earth in a property but not to0 sure about garage?
 
Hi, sorry for lack of info, safe too say my brain was calling for bed time when I started the thread. The garage is not joined on to the house, it's a separate building. Don't think it's going to be a bathroom, just a toilet & sink, never really though about it but if it's done in plastic pipe no earthing is going to be required anyway. The house is TNCS I'm pretty sure.
 
Hi, sorry for lack of info, safe too say my brain was calling for bed time when I started the thread. The garage is not joined on to the house, it's a separate building. Don't think it's going to be a bathroom, just a toilet & sink, never really though about it but if it's done in plastic pipe no earthing is going to be required anyway. The house is TNCS I'm pretty sure.

If the pipework is in copper, or other metallic material then you'll either need to increase your SWA cable to 10mm, or run a separate 10mm CPC for your bonding requirements....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Back
Top