If it's a metal fitting then yes I normally fit the fly lead but if it's a plastic fitting, I don't bother because it's not a reg's requirement.

HOWEVER, if it one of those sockets boxes that's already stuffed full of wires then you make the call - is it value added to shoe horn yet another cable in there?
 
Reg 411.4.2 seems to indicate that the faceplate must be connected to earth via a protective conductor, and so should not rely on earth via the continuity of the screws through a back box lug.

But Malcolm the cpc isn't cut, it's doubled over going from the back box to the faceplate in a continuous run. Would that not comply?
 
Hi Guys
A simple question.
For metal light switches on metal back boxes does the cpc have to be connected directly to the terminal provided on the front plate or can the cpc stay in the terminal in the back box (provided, of course, that there is continuity between the two via the fixing screws)?


But Malcolm the cpc isn't cut, it's doubled over going from the back box to the faceplate in a continuous run. Would that not comply?

Micky I was responding to the OP.

That Regs tells us that All exposed conductive parts must have an earthing conductor, and so as Pete asked, you can't technically take the CPC to the back box and then pick up the earth to the face plate continuity of the screws, regardless of fixed lugs or not
 
[/I]



Micky I was responding to the OP.

That Regs tells us that All exposed conductive parts must have an earthing conductor, and so as Pete asked, you can't technically take the CPC to the back box and then pick up the earth to the face plate continuity of the screws, regardless of fixed lugs or not

That's going to give me some firepower to fire at a guy at work tomorrow
 

Reply to Earthing Metal Accessories in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I think I've found the answers to my questions... I can just do a straight forward wiring i.e. connect the 3 wires from the armoured cable to...
Replies
7
Views
1K
Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
337

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top