E

Etuj

Hi, first post here and after some advice hopefully.

We had a new consumer unit fitted and some additional work, the electrician then tested circuits and got a high earth reading. I think the reading was something in the region of 1.05 and it should be 0.8, he said it was an issue with the earth coming into the house because the reading was high on all the sockets etc.

Apparently we have a TN-S and we should contact the supplier to get this rectified, all good and we called Western Power, they came out that day but the chap was quite dismissive upon seeing the unit and said that isn’t a proper earth which is why the reading would have been outside of the expected range. He also made reference to the bonding saying that an electrician had done that. He could arrange for someone to come out but it would cost us, he quoted something in the region of £130, further to this he didn’t even bother to take a reading!

The chap from Western Power said that the sheath (?) would need to be replaced – so surely this is their responsibility and they would need to repair or replace?
Our electrician made it clear to us from the beginning that anything before the meter is the responsibility of the power supplier, and he cannot touch it.

I am just a bit confused as we were told we shouldn’t be charged, and it seems like Western Power are actually going to be replacing something that isn’t doing it’s job properly – it is an earth?

I am at work at the moment so can’t post a picture but will do later, I would just like someone else’s opinion before we follow this up with Western Power, and then maybe further it they are still adamant that we should pay. Yes we could get a spike put in but I just feel we are being fobbed off by the engineer who came out and it's not right.

Thanks.
 
See below photos, hopefully they are clear enough.

[ElectriciansForums.net] Earthing of TN-S: who should pay?

[ElectriciansForums.net] Earthing of TN-S: who should pay?
 

Attachments

  • [ElectriciansForums.net] Earthing of TN-S: who should pay?
    photo 1.JPG
    69.2 KB · Views: 95
  • [ElectriciansForums.net] Earthing of TN-S: who should pay?
    photo 2.JPG
    57.9 KB · Views: 96
  • [ElectriciansForums.net] Earthing of TN-S: who should pay?
    photo 1.JPG
    151 KB · Views: 100
It looks to me like a DIY TN-S. That earth clamp does not look like the ones a DNO would use. It looks more like a 951 clamp that you would use for equipotential bonding.

If the DNO have said it's nothing to do with them I'd be looking at quotes to get it installed (expensive) and comparing them with an electricians quote to install a system of rods to make it a proper TT system as it appears to have been originally.
 
It looks to me like a DIY TN-S. That earth clamp does not look like the ones a DNO would use. It looks more like a 951 clamp that you would use for equipotential bonding.

If the DNO have said it's nothing to do with them I'd be looking at quotes to get it installed (expensive) and comparing them with an electricians quote to install a system of rods to make it a proper TT system as it appears to have been originally.

But what's with the "greenish" clamp above - seen loads of those around with the main earth connected with perfectly reasonable Ze's.

Tin hat on!

Also what DID the EIC the sparky gave you say about the reading etc??
 
Current reading is 1.05 (I think), holding off on the EIC (certificate I'm guessing?) until the earth is sorted. If not then it will be issued with that higher value.

We have been quoted ÂŁ130 by the power company for them to do the work.
 
Hi, first post here and after some advice hopefully.

We had a new consumer unit fitted and some additional work, the electrician then tested circuits and got a high earth reading. I think the reading was something in the region of 1.05 and it should be 0.8, he said it was an issue with the earth coming into the house because the reading was high on all the sockets etc.

Apparently we have a TN-S and we should contact the supplier to get this rectified, all good and we called Western Power, they came out that day but the chap was quite dismissive upon seeing the unit and said that isn’t a proper earth which is why the reading would have been outside of the expected range. He also made reference to the bonding saying that an electrician had done that. He could arrange for someone to come out but it would cost us, he quoted something in the region of £130, further to this he didn’t even bother to take a reading!

The chap from Western Power said that the sheath (?) would need to be replaced – so surely this is their responsibility and they would need to repair or replace?
Our electrician made it clear to us from the beginning that anything before the meter is the responsibility of the power supplier, and he cannot touch it.

I am just a bit confused as we were told we shouldn’t be charged, and it seems like Western Power are actually going to be replacing something that isn’t doing it’s job properly – it is an earth?

I am at work at the moment so can’t post a picture but will do later, I would just like someone else’s opinion before we follow this up with Western Power, and then maybe further it they are still adamant that we should pay. Yes we could get a spike put in but I just feel we are being fobbed off by the engineer who came out and it's not right.

Thanks.
rite.

Get back on to `western power`...and dont listen to the stupid bird on the end of the phone either bleatin the old script about how its `not our responsibility`....caus its distributers facility...so it certainly IS their responsibility...its the old DNO tac again i`m afraid.

why didnt this electrician liase with them on your behalf?...he should have done...i certainly do as if they sense theres an electrician on the phone they tend to drop the crap....

ask to be put straight through to the area/duty engineer....
 
ÂŁ130 for an earth isn't bad at all. With the amount of work and materials needed to achieve TN levels on earth fault loop impedance you'd probably be looking at around the same amount for your spark to do it.

My advice, pay the ÂŁ130 and get a proper TN-S
 

Reply to Earthing of TN-S: who should pay? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
677
  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top