Earthing Reading | on ElectriciansForums
Discuss Earthing Reading in the UK Electrical Forum area at ElectriciansForums.net
P
paul_sut
Hi all i did a fuse board change the other day and when testing i got a ZE reading of 0.43 and a KA of 5.93 why would the KA be so high, also zs failed on all circuits for breakers. This is TNS. what would any one recommend??
i've just got one of these new megger mft1710 and i pressume i have i think it came up 593A? also why would my zs fail for example for the ring 32a breaker i got 6.29??
In red - are you sure? Your OP said 5.93Ka - which is it?
Your ring may have a problem, what were your "dead" tests like? Or is it all circuits?
Loose connection somewhere in the original install? I had a zS of 4000 once!
There is a few fixes tho, you could add some bonding to create parallel paths, this may bring your zs down
You could rewire it with a bigger CSA cable to lower the r1+r2 value
Or as you will now have rcd protection you can have a maximum of 1667ohms but if it's over 200ohms check it out!
Just another thought if you were taking the Ze then the main earth would of been removed from the earth terminal, once that was replaced to start doing zs's could the terminal screw cross threaded and backed off abit?
All rcd protected now but is old house all decorated etc dont want disturbance if you know what i mean. main bonding all done to water and gas 10.0mm, main earth 16.0mm to sheath. Another reading i got was the boiler which was new circuit tight connections etc and the zs was 6.41 on 16a breaker.?
Mmmmm wierd one, has the whole wiring been inspected?? I.e is the ring final results ok? It could be a case of a DIY job few jbs spuring of the 2.5 in 1mm Somthing on the lines of that?
Reply to Earthing Reading in the UK Electrical Forum area at ElectriciansForums.net
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Yes, probably overthinkig, thanks.