P

paul_sut

Hi all i did a fuse board change the other day and when testing i got a ZE reading of 0.43 and a KA of 5.93 why would the KA be so high, also zs failed on all circuits for breakers. This is TNS. what would any one recommend??
 
Well no your readings should be 0.23 if you did a figure 8 at the board and tested at each point on the ring?
Something don't add up to me and you need to have good results and thorough tests to prove the main earth is at fault, especially if you are getting good readings of .43ohms with the Ze?
 
I think as for the ring reading, you should go to each point of use, and take the highest reading, now if there was a spur of a reasonable length off the ring the ohms would be higher on this than a pure ring and this would be the value entered on the cert as proof of meeting the disc time.

J
 
But you have the choice as to whether you should power it up, this whole thread worries me.

J

With additional proTection by rcd is in place then 1667 ohms is the highest zs, we have 6ohms here, that's 1661 ohms less that the maxium.....although that is totally unrealistic zs and should be investigated but even then the regs states anything over 200ohms. So he has done everything to bs7671 here.
 
Last edited by a moderator:
With additional proTection by rcd is in place then 1667 ohms is the highest zs, we have 6ohms here, that's 1661 ohms less that the maxium.....although that is totally unrealistic zs and should be investigated but even then the regs states anything over 200ohms. So he has done everything to bs7671 here.

Sorry in advance! Thats a poor attitude to take. I can honestly say that i'v never left an installation like that. Something is obviously wrong so it needs sorting end of.
 

Reply to Earthing Reading in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Yes, probably overthinkig, thanks.
Replies
6
Views
599

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top