I'm afraid I didn't entirely follow your post but it sounds like you're considering disconnecting a bonding strap or wire which is kinda worrying. What does the 'earth sparking' refer to in the title of your post? Did you disconnect the earth and it was sparking?
I can give you some general advice;
Never ever disconnect any part of the earthing arrangement or its associated bonding when the installation is still live. In some installations large earth currents could be flowing which could kill you and anything connected to the section of earthing you disconnect is likely to rise to a dangerous touch voltage which could kill someone else as well.
The whole idea of earthing and bonding is to create a zone or area in which is everything is bonded together to hold it at the same potential and the entire zone is earthed to hold it at zero volts with respect to ground. If you disconnect one area of the equipotential zone then dangerous voltages can develope between items in the same vicinity leading to electric shock.
If you're trying to extend the equipotential zone then it must be done from the MET, not by running wires from the frame of the building.
Maybe you can explain further exactly what it is you're trying to achieve and how you're thinking about going about it or maybe attach a sketch to help clarify.