Agreed,does anyone still run a separate tail from a socket earthing terminal to a metal wall box ?
Yes, it's how I was taught as an apprentice and I'm a stubborn bugger.
Agreed,does anyone still run a separate tail from a socket earthing terminal to a metal wall box ?
No, you should never take an accessory off without the circuit being isolated. If It's isolated then there's nothing that can bite you therefore there is no need for the fly lead
By identifying the circuit and carrying out the safe isolation procedure.But a circuit is not isolated until it has been proven dead with a suitable tester. So how do you get the tester in to the lightswitch without taking it off the backbox?
you do thisBut a circuit is not isolated until it has been proven dead with a suitable tester. So how do you get the tester in to the lightswitch without taking it off the backbox?
But a circuit is not isolated until it has been proven dead with a suitable tester. So how do you get the tester in to the lightswitch without taking it off the backbox?
Find the correct MCB (by a process of elimination if necessary, we've all been there) turn it off and then test. You've taken reasonable precautionsBut a circuit is not isolated until it has been proven dead with a suitable tester. So how do you get the tester in to the lightswitch without taking it off the backbox?
ok trev what do you do when you have removed all the fuses and your snips go bang.Find the correct MCB (by a process of elimination if necessary, we've all been there) turn it off and then test. You've taken reasonable precautions
Your snips should never go bang because you should always follow the safe isolation procedure. If you're in an upstairs flat then I appreciate that you could chop the wrong cable and make them bang but......ok trev what do you do when you have removed all the fuses and your snips go bang.
sorry mrs ive just chopped your neibors lighting cable lol
funny as **** when you see someone do it
it wasn't in this case thats what made it amusing, someone was stealing there lecky (terrice)Your snips should never go bang because you should always follow the safe isolation procedure. If you're in an upstairs flat then I appreciate that you could chop the wrong cable and make them bang but......
By identifying the circuit and carrying out the safe isolation procedure.
Back to my question.
If a metal back box is deemed to be an exposed-conductive part, then why not the armour on an SWA cable?
I would say that it's because there are two layers of insulation between the conductors and the metallic part (insulation and sheathing inside the swa).Back to my question.
If a metal back box is deemed to be an exposed-conductive part, then why not the armour on an SWA cable?
but once the faceplate fixing screws are fitted, it then becomes "exposed".Of course it's obvious, the metal back box cannot normally be touched, without the use of a tool and the removal of earthed screws, whereas the armour can be touched simply by sliding a gland boot down. Something that can occur without human intervention.
Personally, it depends upon the use of SWA as to whether the armour needs earthing, its good practice to earth it in my opinion.
T&E and SWA can't be compared, either are chosen to suit the design of the installationWhat happens if the basic swa insulation fails, is there any supplementary insulation? The bedding of SWA is PVC, are the live parts of this cable any worse than that of T/E. Is there any supplementary insulation between cpc and basic insulation in T/E?
Cheers.
I would say its imperative to earth the armour of an SWA.
T&E and SWA can't be compared, either are chosen to suit the design of the installation
I think your missing my point, look at the definition of an exposed conductive part, it states basic insulation, swa has basic and supplementary insulation.
Does the armour need connecting to earth, in many instances but not all.
Cheers
PreciselyIt always needs connecting to the earthing system of the installation it is fed from.
One purpose of the armour is to connect any metal object penetrating the cable with earth before it makes contact with any live conductor.
It always needs connecting to the earthing system of the installation it is fed from.
One purpose of the armour is to connect any metal object penetrating the cable with earth before it makes contact with any live conductor.
Okay, lets say we use swa instead of T/E surface mounted, there is no requirement for an earthed sheath, just because its there, where in the regs states it must be earthed, Reg numbers?
If the basic insulation fails Dave, will the armour become live or will the supplementary insulation prevent this. So how does it meet the definition of an exposed conductive part, any Regulation numbers would be good?
Now if the cable is buried, thats a different matter.
So surface mounted, into plastice enclosure via plastic gland, boot over end of cable protecting ends of cable within enclosure. What are the Regulations requiring the armour to be earthed?
Cheers
No at the very least on smaller sizes of SWA there is definitely a solid insulating sheath external to the insulated cores !
So IMO that is insulated AND sheathed.
Well I've stripped hundreds of SWA ends and the material under the armour is just like the sheath of flex, and it's not conductive is it ?!
Well we must be using versions of SWA from different universes Dave. :confused5: I'm thinking 1.5/2.5/4/6mm 3core , and that sheath is as tough as flex sheath.
What supplementary insulation? The conductors are insulated, they are then bound together with tapes or an extruded bedding, armour laid over that with an outer PVC serving.
There is only one insulation layer.
It is not an exposed conductive part, I have never suggested it is! But the cable is designed to be installed with the armour earthed, if it is not then it is not being installed as it is intended.
The cable is designed, tested and approved for use under the British standards referenced in bs7671. That approval will have been given with the armour earthed as it was designed to be.
The bedding? It's carries no insulation rating whatsoever, it's purpose is to give the cable shape and prevent the armour coming in to contact with the insulation of the cores.
You say it is just like the sheath of flex, which particular flex are you referring to? I can't think of any flex which has a sheath that soft. It's irrelevant anyway as the sheath of flex is also a sheath and not insulation
Dave the Extruded bedding compound used by cables to BS5467 is PVC, are you suggesting this has no insulating properties?
So there is no requiremnet within BS7671, i have various Manufacturers data, where are you finding reference to the armour requiring earthing, which manufacturer?
Cheers
Yes it is sometimes PVC, it can also be a string and tape but this is less common these days. but it is not tested or rated for any voltage withstand.