What PVC?

Yes, not all PVC is the same! The bedding and sheath are both made of PVC, if you have a proper look at it next time you strip some you will notice that it's not the same. The density, strength, flexibility etc are different due to a lower grade (cheaper) being used for the bedding than for the sheath
 
but once the faceplate fixing screws are fitted, it then becomes "exposed".
So by using screws which are earthed via the faceplate, the back box becomes exposed requiring a fly lead to connect it to the face plate so it can be earthed?
 
I always connect the earthing fly lead to back boxes I install, it's easy to do if done before installation of the box, takes 10 seconds and 4 inches (100mm) of earth cable. In fact, I used to carry pre-cut lengths of cable for just this purpose. I also earth both ends of the SWA, it doesn't take long and I think it's good practice.
 
I always connect the earthing fly lead to back boxes I install, it's easy to do if done before installation of the box, takes 10 seconds and 4 inches (100mm) of earth cable. In fact, I used to carry pre-cut lengths of cable for just this purpose. I also earth both ends of the SWA, it doesn't take long and I think it's good practice.
thats a good way to do it, earth lead when you first fix i mean
 
As stated the bedding (although it may be made from insulating material) is not tested as insulation. Likewise the sheath of T&E; flex etc. is not tested as insulation.

That is not its purpose.

Also, in an SWA the bedding is not intended to be used as a sheath, so couldn't be run free as an insulated and sheathed cable, as it isn't and therefore must be within the enclosure if the sheath and armour has been removed.
 
Certain industrial installation designs require that earthing systems are separated from source supplies due to the requirement to maintain a "single point earthing system".
For example some signalling rooms on railway installations are provided with a earth that forms part of the signalling system and is totally separate from the main supply earth.
Typically the design for those installations will specify that the sub-main SWA cable supplying that location is only earthed at the origination of the supply and that the load end is terminated in to a "insulated cable gland".
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Earthing SWA at both ends
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
88

Thread Tags

Advert

Thread statistics

Created
atm84,
Last reply from
Big Sausage,
Replies
88
Views
43,635

Advert

Back
Top