W

wolfiehogan

hi guys,
just a quick question for somebody.
the other day when i was glanding an s.w.a at both ends i was told that it was wrong and that you where only meant to gland one end off the swa as if you gland both ends you are creating a ring?? is this true or can some one help me out
 
i have heard this before, i was told that when doing a tt system on site temps, u are only supposed to earth the supply end of the cable so that under a fault you wouldnt create a potential on other cabins. i think its best to earth the lot, then you allways have a path to earth. but i dont know
 
you can use flylead. Some glandplates in industrial eqt are threaded, so you do not need to use a banjo. You can also scrape away the paint on the metal enclosure you are glanding to and then bolt the banjo to the accessory. if yo do this, then make sure you paint any exposed metalwork after you have glanded the cable, to stop corrosion.
 
You only need to earth the gland at both ends if you are using the armour as the CPC, however you must always earth the armouring at at least one end. There is nothing wrong with earthing at both ends even if your using an internal core or a seperate cable as the earth, The exception to this would be when running a supply and having a TT installation at the end, in which case you need to make sure that there is no earth connection between the supply and the TT side.
 
ya assuming there's a separate cpc you complete the parallel fault path with the banjo at both ends-no harm done

i think best banjo if boards are metal anyhow

-except for the 'conversion to tt ' scenario
 
hi guys just a bit extra to my question earlier. if i was to supply a garage/shed beside a house with a swa cable. would the garage be part of a tt system?? should i bury an extra earth rod at the garage?? i would have a seperate cu in the garage too. in the past i have glanded both sides of the swa and would have an internal earth inside the swa. i dont bury an other earth rod is this ok?
 
Last edited by a moderator:

Reply to earthing swa question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
145
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
944
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
725
loz2754
L
Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
360

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top