Is it acceptable to put plastic screws in switches when there is no earthing to them to satisfy eicr?
 
Not in my opinion, no. The EICR shows the switches as not being earthed so fitting nylon screws doesn't resolve it. Assuming this is a dwelling who is going to monitor the installation to ensure the nylon screws are not replaced with metal?
 
Is it acceptable to put plastic screws in switches when there is no earthing to them to satisfy eicr?
The earth cpc must be securely connected to the back box terminal where a plastic switch is installed. When a metal switch is installed, the earth cable must be connected directly to the switch earth terminal
 
It is as this is like implementing an ad hoc Class II installation.
So it's OK to use a backbox with isolated lugs - even though the switch and the wiring in the box won't meet the standards for Class II. Plus the user could just replace the switch with a metal.one.
But it's not OK to use plastic screws because the user might replace them with metal ones.
Either both are OK, or neither are. To say one is and the other isn't "because the usr could change something" is being inconsistent.
 

Reply to earthing switches in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Hi all. Try to keep this nice and short. Had an EICR fail on a health centre due to corrosion on main supply which was causing high Ze values...
Replies
0
Views
184

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top