Hello, I wonder if there is anyone here to help me out. Thanks in advance for the help.
Ok. I am doing electrics on 6 metal containers in community fields( I know, I don’t like them metal boxes too), I got it all under control, but there is little thing what buggers me. I kind of finding trouble working out the earthing arrangements. I know, stupid me, forgot to take the pictures, but the picture in words is:
From the first view it seems like TN-S (it has the earth cable coming out from the sheathing of the incoming supply cable, but on closer look I found that it has another earthing cable coming to MET, and when traced,I found it attached to the rod, so maybe TT then.
Measured Ze from the sheath only, it came up as 0.25 ohms (lovely),measured from electrode only, it came as 525 ohms ( up’s), measured them both together, it came as 0.27 ohms. Lookslike rod is worsening the Ze for me. I thought just to get away with the rod,but something not right here, because I Have the 30 mA RCD before the whole installation too, which is strange too.(100 mA would be sufficient and then down to 30 mA on the final circuits)

So my questions are:

· What earthing arrangement I have:
· TN-S (earthing from sheath)?
· TN-C-S( some sort of converted and because is so low reading)
· TT ( as per earth rod and RCD )

Thanks again for your input guys, and I need it sort of ASAP, started today and planning to finish on Friday, so realy need to work this out.
 
Well the only DNO cable i know where the earth comes directly off the sheath, is the older PILC cable. These days the DNO's's will use Split concentric cables in there legs up to the TN-S service heads. I doubt these pillars have been in place since the time of PILC's, so i'm a little confused now. Shame you can't post a photo or two. A picture can explain many questions... lol!!

thanks for reply, i dont think it is PILC, there is no lead sheath, probably it is more like split concentric as you say becouse of the fine copper strands visible on the sheath, I promise to do pics tomorrow.
 

Reply to Earthing system question please??? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
707

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top