Joined
Jul 9, 2011
Messages
151
Reaction score
12
Location
Cardiff, but work SW
It is possible to have both TN-S and TN-C-S supplies from the same transformer. For example, the sheaths on some underground cables corrode and stop providing good earth connections, and so homes where "bad earths" are found get converted to TN-C-S
 
Possible maybe, but is it legal? Not according to 543.4.9. Depending on the routing, it takes away all the pros with a separate PE/N. I guess the cost of digging is a factor...
 
It's possible to get two different supplies off one transformer . But as far as getting a TNCS supply from a TNS installation , I don't think that's possible. If the cable got that badly corroded that the Neutral was touching the earth, you would still have a TNS system, just one with a fault! The consumer wouldn't know any different.
 
It is possible to have both TN-S and TN-C-S supplies from the same transformer. For example, the sheaths on some underground cables corrode and stop providing good earth connections, and so homes where "bad earths" are found get converted to TN-C-S

YES it is possible, and all too likely too!! When the DNO earth a neutral at the T off joint to a house, or any other joint come to that, they do not include the lead sheathing as part of the N-E connection. In fact they will keep the continuity of the lead sheathing in place. You need to remember also, that it may only be a section of the DNO supply cable that is affected, maybe due to a higher corrosive soil or industry chemical saturation. The rest of the cable could be just fine... It would cost the DNO's an absolute fortune to PME every installation on a cable run, just for the sake of a short section of cable turning bad!!

Your not mixing the two TN systems at the service cut-out, and you will generally comply with whatever DNO earthing arrangement is presented to you!! Where a TN-S system has been converted to TNC-S hopefully the DNO remove the earthing conductor from the lead sheath and insulate with amalgamating tape any exposed lead sheathing... Generally they remove the sheath earthing conductor but don't bother insulating the exposed lead sheathing!! lol!!

This is where the difference lies, between a PME and TNC-S, DNO supply. PME systems will have every or almost every joint PME'd, anything much less than that, will be classified as a TNC-S supply...

Not sure why anyone would think it's not legal, or quote BS7671, as this will only be affecting DNO owned equipement, and they certainly don't follow BS7671!! They tend to make there own rules as they go along!! lol!!
 

Reply to Earthing system , TNCS off a TNS? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
176
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
1K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top