We've have been running an earth to the array and bonding each seperate rail together. We were actually discussing this very thing on site today where we were considering linking between joiners on the rails.
 
@BiggsSolar - hadn't thought of that element!

linking between joiners on the rails.
I'd definitely formally join the rails and not assume an electrical connection.

@malcolmsandford, the flow chart clearly states that if it's PME you mustn't take PME outside the equipotential zone.
However just because it's outside the building fabric doesn't mean it is outside the equipotential zone, take the case of solar thermal (with copper pipes linked to earth) or a metal clad, metal framed agricutural building, in both cases you are clearly extending the equipotential zone outside the normal building fabric, and putting it within reach of other "exposed-conductive parts and extraneous-conductive parts"

The question still is what are people doing and what's best practice..
 
I have done 2 now where they had to be earthed. Both were bonded using external earth clamps to each rail and bonding between the rails and then to an earth rod because both were PME.
 
Should also say, if I was to come across a different type of earthing arrangement, then I would follow guidelines and bond into the main earth terminal.
 
We've done a lot of transformerless inverters and I tend to bond to across the rails ie if there is four rails for a portrait system these have all been TT ,and the array earthed to a rod
as i posted on another thread i have tested for voltage on the Tl jobs we've done and there is always a voltage of >50v (highest being 108v) on the frame turn the inverter off and it vanishes ,i tell our customers to turn the system off when cleaning panels or working near the array
I did have a pdf explaining this which was possibly from Sma so i'll have a look for it
 
Last edited:
Can I ask where this grid comes from? ............is it from the MCS.

The point about the exported earth of a PME system is that any extraneous conductive parts in an out building or now if you prove that a array frame is one, then you need to bond the ECP back to the MET.

In many outbuildings that are several metres from the building it can be cost prohibitive to run a 10mm bond many metres back to your MET, and so in these cases it is better to make the outbuilding or frame a seperate TT, but AFAIK there is no regulation prohibiting you exporting a PME earth and bonding the ECP to the MET.

It just rankles a little when I see something like that chart that prohibits something that is not prohibited.
 
the pdf i was talking about is titled capacitive discharge currents from Sma this explains how the voltage transfers to the array,hence the need to discharge to earth with Tl inverters,I'm sure i've got another regarding earthing the array,so i'll keep digging
 
the pdf i was talking about is titled capacitive discharge currents from Sma this explains how the voltage transfers to the array,hence the need to discharge to earth with Tl inverters,I'm sure i've got another regarding earthing the array,so i'll keep digging

I can understand when your not using a transformer invertor as your not using seperation via the transfromer, that there is a chance that a fault on the DC side can easily be transferred into the the AC system, if the array frame is not bonded.
 
Thanks for the post Worcester I have to cede that your knowledge of PV is far above mine. I just take exception to the fact that a body as categorically stated that a PME earth can not be exported, and that is just not true.

As I posted providing that certain requirements are met there is no reason why a PME earth can not be so.

I'm sure you saw that I was arguing here a week or so ago why the ECA thinks that a PV system that is installed in a domestic situation on a split RCD board contravenes regulation 314.2, as I can not see why that is correct.

I feel that there is a lot of uneccessary red tape concerning this part of our industry, and that certain organisations are trying to re-write the basic electrical fundimentals. It is a new branch of our industry but when section 710 for medical equipment comes into force I wonder also how many "bodies" will try and put their interpretations on the Regs.
 
@malcolmsandford, no problem, appreciate the debate and being challenged once in a while :)

The problem we have is that the 'inspectors' are not technically minded, they are process driven. Some don't even like a variance in the placing of an isolator (even when the drawings show two variations!) ...

The PV industry and certainly the regulations / guidelines are really only now being tested (just talk to the DNO's, some are still strugling to understand FITS 15 months on)
 
Not needing to have bond any arrays (yet) we had discussed similar to Biggssolar only using the fixing bolt, roof anchor to rail rather than rail joiner but then we also discussed where rail slip joiners are used for expansion and considered these as not an effective means of continuity as only one end is fixed to the rail and the other floats inside the rest of the rail. So as and when we need to we will use a additional one turn bolt into the rail as a specific bonding location and again on a floating rail. We would also bond every rail. We use Schucco system by the way.
 

Reply to Earthing the Array - Practically in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

Need to crack on to get most from this year :cool: BTW if you are thinking about adding to the strings later, i.e. add more panels to existing...
Replies
6
Views
930
I think I've found the answers to my questions... I can just do a straight forward wiring i.e. connect the 3 wires from the armoured cable to...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top