I've run an earth 10mm to main water supply in house and there is currently no seperate earths run to bathrooms. All circuits are rcd protected and when i checked continuity at sink pipes using flying lead the reading was fine but when i checked at the shower there wasn't any continuity. Checked above the shower and noticed some of the pipes were plastic. I've been told by someone now that I need to run a seperate earth to the shower?? Is this correct?
 
Hi, steve, thanks for your reply. I should have stated it ain't an electric shower and that it was not the shower I tested but the shower copper pipes. Sorry about that. Does this change anything?
 
If all circuits in the bath/shower room are RCD protected,and max disconnection times are met,and you have a continuity reading of <1667 ohms between conductive parts within the bath/shower room and metallic pipes entering the bath/shower room you do not need to supplementary bond. If metallic pipes within the bath/shower room are supplied by plastic pipes there is no need to bond.There is no requirement for continuity to any other pipes/sinks etc outside of a special location as defined in section 7 of the BRB other than main bonding incoming services......all of this can be found in the OSG.
 
Last edited by a moderator:
If all circuits in the bath/shower room are RCD protected,and max disconnection times are met,and you have a continuity reading of <1667 ohms between conductive parts within the bath/shower room and metallic pipes entering the bath/shower room you do not need to supplementary bond. If metallic pipes within the bath/shower room are supplied by plastic pipes there is no need to bond.There is no requirement for continuity to any other pipes/sinks etc outside of a special location as defined in section 7 of the BRB other than main bonding incoming services......all of this can be found in the OSG.

As far as i can see the pipes are plastic in the loft to above the shower where they are changed to copper. I think (not sure) the pipework before plastic is copper as well, if that makes any sense? Seems to be this part was done in plastic as it would have been a pain for copper pipework to be put in that angle. Is this normally a done thing?
 
Last edited:

Reply to Earthing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

M
  • Article
Intermittent bad smell Hi I have an intermittent bad smell that's really hard to pin down, I was wondering if I could get your thoughts on it...
Replies
0
Views
229
MatthewG
M
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
628

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top