Hi guys,
Doing some work in a rural area. The client is having an office built behind his house. It consists of a bathroom/shower room, kitchen, and office space.
The wants electrical feed taken from the house and it having a trench dug to run all services.
The house is on a TT, and has it owns earth rod.
Was going to run a 2 core 25mm SWA from a 80a wylex isolator in main house and run that straight into CU in office.
Questions:
1: Can i use the earth from the house, through the sheathing of SWA, if the Ze is less than 200Ω when tested at the office end, or do i need to install my own earth rod?
2: Does the SWA need to be a certain distance in the trench away from other services?
3: Is 0.6m still the correct depth for a buried cable?
Thanks