I have to do some lightning protection on a building and need the test cert issued for it , anyone have such a thing, surely there must be in this over paperworked industry.
 
I have to do some lightning protection on a building and need the test cert issued for it , anyone have such a thing, surely there must be in this over paperworked industry.

There's a lot more testing to be done on Lightning Protection systems, than just the earth rod values.
 
Sorry for the delay Dasersc,

Depends on what type of lightning protection system your working on.... I'll take it, that it's a conventional air conductor/down conductor system. Does the system have air conductor spikes, or will just rely on the flat tape as the air conductor??.

On this system yes it's basically Rod tests and resistance tests. If it's a new installation then a thorough air conductor routing inspection should be performed, to make sure there are no flash-over points and that there is never less than 30cm between parallel or adjacent air conductor tape or cable runs.. And to make sure that the flat tape/cable fixings are adequate in number as to be suitably braced for potential lightning strikes....

All through and crossing connections on air conductors, as well as connections to mechanical roof plant, such as AC units, roof fans and the like must be solidly made and have a maximum resistance of .05 ohms, ...which to be honest is really generous, actual readings should be much lower than this!!! These tests normally conducted with a low ohm or ''ductor'' type tester that injects current/potential into the connection/joint under test. Down conductor test points must also be tested to the same level, after the rod testing and with the removable link reinstated...

The rods in such a system all need to be tested individually, and then tested combined. The combined Ra value is the important result. In the UK that Ra value must be no more than 10 ohms (Max). Very few such installations will have such a high combined value...


Don't forget to check there is a suitable bonding connection from the LP system to the buildings electrical MET, and don't forget to disconnect that bonding during your LP system testing...
 
Last edited by a moderator:

Reply to earthrod test cert?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

We wouldn't be at all surprised I have been a QS for 25 odd years.
Replies
7
Views
817
Hi If a new build has solar and battery fitted, but no paperwork or sign off has been completed, what are the implications? Do you need a mcs cert...
Replies
0
Views
331

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top