OP
claypole
http://download.sma.de/smaprosa/dateien/7418/TempDerating-UEN103910.pdf
The above download finally crystalised this for me, with some excellent charting to demonstrate the logic. Until reading this I was very firmly decided that there was no good reason to size the inverter smaller than array except initial cost. I'm now wholly committed to the opposite view. For my system using SB4000TL and 245 Sharps the sweet spot, in terms of kwh/kwp was something like 4.9kwp, bearing in mind the inverter max dc is 4.2 kw. I found this almost impossible to believe until I read the above download and understood the logic.
The 4kw FIt band doesn't prevent you exceeding 4kwp. It may well be that doing the sums shows that the larger array on a lower FIT rate band will still have the best rate of return, although in practice this is perhaps then governed by the DNO connection. However, from Ted's excellent DNO/G83 thread it seems most of the DNO's are swinging round to using inverter output figures, so provided they'll accept 4kw and G83 at the particular installation site that problem is removed. I also live in hope that Ofgem may at some point issue guidance that TIC may be based on inverter max dc input (albeit that's 4.2kw on the 4000TL). Personally, I've gone down the route of 3.92 array now, to extend to 4.9 after 12 months, all through 4000TL. Based purely on the maths for max rate of return.
The above download finally crystalised this for me, with some excellent charting to demonstrate the logic. Until reading this I was very firmly decided that there was no good reason to size the inverter smaller than array except initial cost. I'm now wholly committed to the opposite view. For my system using SB4000TL and 245 Sharps the sweet spot, in terms of kwh/kwp was something like 4.9kwp, bearing in mind the inverter max dc is 4.2 kw. I found this almost impossible to believe until I read the above download and understood the logic.
The 4kw FIt band doesn't prevent you exceeding 4kwp. It may well be that doing the sums shows that the larger array on a lower FIT rate band will still have the best rate of return, although in practice this is perhaps then governed by the DNO connection. However, from Ted's excellent DNO/G83 thread it seems most of the DNO's are swinging round to using inverter output figures, so provided they'll accept 4kw and G83 at the particular installation site that problem is removed. I also live in hope that Ofgem may at some point issue guidance that TIC may be based on inverter max dc input (albeit that's 4.2kw on the 4000TL). Personally, I've gone down the route of 3.92 array now, to extend to 4.9 after 12 months, all through 4000TL. Based purely on the maths for max rate of return.