Good Evening All. First question on site so apologies for bad formatting.
Am interested to know best work around for testing the off peak side of a split load board fed by a teleswitch meter running economy 7 storage heaters. Able to perform dead tests but no power until after midnight so cannot test Zs or the RCCB that governs the radial circuits. Tenant cannot function test the RCCB either. Other half of split board fed separately from supplier side meter tails.
Any clues or hints very much appreciated - thank you in advance
 
hi would use r1 + r2 value to calculate zs (ze+r1+r2 =zs) as for rcd is no way of testing it unless you go round at midnight just note it on certificate as not tested
 
Thank you for your reply. Can I temporary feed to the intake on the off peak RCCB without it affecting the teleswitch or only to the supply side on the individual radial mcbs? Would ideally like to function test the RCCB whilst i'm there. Do not know anything about how the teleswitches behave only what I have gleaned from this forum.
 

Reply to Economy 7 circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
257
  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top