After a bit of advice. Have a 630A MCCB feeding a DB, it's fed with 4 x 300mm single core, non armoured HO7 cables and a 185mm earth. The DB is GRP and plastic compression glands have been used. The main panel has an aluminium gland plate and brass A2 glands have been used, however, the lock nuts are steel. Will this cause issues, do the lock rings need to be changed to brass also?
 
After a bit of advice. Have a 630A MCCB feeding a DB, it's fed with 4 x 300mm single core, non armoured HO7 cables and a 185mm earth. The DB is GRP and plastic compression glands have been used. The main panel has an aluminium gland plate and brass A2 glands have been used, however, the lock nuts are steel. Will this cause issues, do the lock rings need to be changed to brass also?

Any metal that completely surrounds a single core cable should be non-ferrous, that includes lock nuts, so in my opinion these should be changed to brass.
I have always kept the lock nut the same material as the gland on single core cable, just something I was told years ago but never actually fully knew why. The reason I asked is because they are going to be pig to take back off and swap and wondered whether anyone had any experience of it.
 
I have always kept the lock nut the same material as the gland on single core cable, just something I was told years ago but never actually fully knew why. The reason I asked is because they are going to be pig to take back off and swap and wondered whether anyone had any experience of it.
I’m afraid that’s what needs to be done, especially on high current circuits such as this.
 
It will be easier to replace the lock nut on singles, assuming there is ready access than a multi-core cable.
I agree, multi core would be worse. There is however a plastic gland plate half way down the enclosure which cables run through an additional plastic compression gland for support. The lug probably won't fit through the plastic compression gland so would have to cut the lug off slide it back down through the plastic gland and then swap the lock nuts.

Nowhere near impossible just a lot of extra work, hence wanting a bit of clarity as people have different opinions on it. Would ideally like to leave the steel ones place but obviously wouldn't if its going to be dangerous.
 
Is it already in use / under normal load?

If so just check to see if the nuts appear noticeably hotter than the cables.
It is, its suppling a PV system which appears to have been installed late last year. At the time I was there it was cloudy so not much current was flowing back through. Guessing when summer comes round these cables will get hotter as more current flows back, which will heat the lock nuts? Wasnt sure whether the actual glands being brass, gland plate being aluminium and cable being non armoured would have any bearing on potential eddy currents.
 
If the lock nuts are only holding the gland in place and there is no undue force on them from the cables you could undo the nuts and carefully put a cut through them and hope they thread back on.
 
I thought of that too. But somehow I doubt they would hold IMHO.
Depends on how tight they need to hold the gland but I agree they will never be tight. If they only need to hold the gland in place to support the cable entry you could run some Loctite thread sealer into them.
 

Reply to Eddy currents?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top