Hi,
This relates to our planned PV installation. The G99 application came back outside SSEN's limit for voltage rise, which for property connected at 240V is 1.3%. They will, for an estimated £2K, "look to" change our transformer to drop voltage in normal operation.
"Alternatively we can look at tapping the transformer again. We tap the transformer by 2.5% reducing the voltage from 240v to 234V, this then increases the volt rise limit from 1.3% to 4%, and in turn this reduces the volt drop limit from 7% to 4.5%."
If they can do this, our proposed system would be within limits.
What concerns me, apart from cost and the fact they can't guarantee it will even prove possible, is the possible efect of this permanent voltage reduction. The characteristics that make this necessary are the length and size of the service cable. These also mean larger voltage drops under load, compared to better supplies.
Alternatively and with no change they would permit 4kW export limit as this would not exceed that 1.3%
Any thoughts?
This relates to our planned PV installation. The G99 application came back outside SSEN's limit for voltage rise, which for property connected at 240V is 1.3%. They will, for an estimated £2K, "look to" change our transformer to drop voltage in normal operation.
"Alternatively we can look at tapping the transformer again. We tap the transformer by 2.5% reducing the voltage from 240v to 234V, this then increases the volt rise limit from 1.3% to 4%, and in turn this reduces the volt drop limit from 7% to 4.5%."
If they can do this, our proposed system would be within limits.
What concerns me, apart from cost and the fact they can't guarantee it will even prove possible, is the possible efect of this permanent voltage reduction. The characteristics that make this necessary are the length and size of the service cable. These also mean larger voltage drops under load, compared to better supplies.
Alternatively and with no change they would permit 4kW export limit as this would not exceed that 1.3%
Any thoughts?