On an EIC what would you record as the origin of supply details if the sub board the circuit has been installed on is its self supplied from a sub board.

Long story but we have had some work done by a contractor who used a subby for the electrical install and he has but the local board that the circuit is feed from. Now I have always thought that it should be the supply intake. Am I correct?

This is just one of a few issues with the certificate and this is supposed to be a niceic approved contractor.
 
Yes you are correct. As you well know the origin of supply details are taken at the origin of the install and not a sub supply. Zdb and db pfc values belong on the schedule of test results.
Did they not have access to the origin ? I can well imagine that in a large commercial or industrial install (which I'm assuming this is) they wouldn't have access to isolate the entire install to test, but I'm sure you would have records of the relevant data had they asked.
 
Yeah I will be making a phone call on Monday. Thanks for confirming my thoughts, don't really do many EIC and mainly reactive maintenance. Last one was probably 5 years ago!! At least I can go back to them without making myself look a numpty.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Devon

Thread Information

Title
EIC origin of supply
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
Paul651975,
Last reply from
Paul651975,
Replies
4
Views
3,226

Advert

Back
Top