As far as i remember from my day's in an industrial environment, virtually every 3 phase socket circuit were fed via BS 88 fused 3 phase DB's. lol!! Now as far as i know, EICR's are conducted to conform with BS 7671. I can see things getting very confusing if you start applying and/or including other regulations to a BS 7671 EICR format!!
 
Which specific problem do you have with the circuit:
That unlinked SP fuseholders are the means of isolation or switching?
That the fuselinks installed are inadequately rated (e.g. for voltage) to protect the circuit?
Or that the OCP is not linked across the phases as it would be in a TP MCB?

If the latter, I am not sure the NICEIC people understood your query. You would be in trouble if you tried to C2 every TP circuit fed by HRCs.
 
Check the EAW regs, I am fairly certain that you should have a means of disconnecting all your line conductors at the same time. i.e 3 pole linked switch.

E@WR 12 (2) In paragraph (1), “isolation” means the disconnection and separation of the electrical
equipment from every source of electrical energy in such a way that this disconnection and separation
is secure.

Nothing about simultaneous disconnection, so just pull the fuse...times 3, and hide them!
 

Reply to Eicr 1361 fuses 3phase circuits from db in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
926

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
513
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top