Hello,

An EICR unsatisfactory is claiming all the lights are not fire rated and "do not comply BS7671 too".

Can be classified as C2 if they are not fire rated?
 
Last edited by a moderator:
Yes they are on the ceiling
But is the ceiling
Yes they are on the ceiling
But is it classed as a fire ratted ceiling normal not require in a single dwelling such as a house . If the cieling is just single 8mm plasterboard then it is not a fire barrier. Then fire ratted down lights are not required . If there is a flat above then it may require to be fire ratted
 
I might code them in a bathroom if within zones as to regards their IP rating, but nothing to do with fire rating.
 
Tell us about the property. Flat or house for a start.
The report should theoretically have enough information for someone else to fix it - does it say how many lights, or where, and how they do not comply with (presumably) BS7671 ?
 
Tell us about the property. Flat or house for a start.
The report should theoretically have enough information for someone else to fix it - does it say how many lights, or where, and how they do not comply with (presumably) BS7671 ?I

Tell us about the property. Flat or house for a start.
The report should theoretically have enough information for someone else to fix it - does it say how many lights, or where, and how they do not comply with (presumably) BS7671 ?
It's an upper flat. The lights are in bathroom(8), kitchen(6), lounge(6), landing(3), bedrooms(4). It doesn't mention why they don't comply, there is only an extra note with "lights have signs of over heating surrounding"
 
Tell us about the property. Flat or house for a start.
The report should theoretically have enough information for someone else to fix it - does it say how many lights, or where, and how they do not comply with (presumably) BS7671 ?
The lights actually tested are 3 in the kitchen, 2 bathroom, 2 hallway, 2 bedroom and 2 lounge
 
Are you saying there are other flats on the same floor, additionally I was asking is there a common loft area, if so the ceiling may be a fire barrier.
 

Reply to EICR - C2 on kitchen/bathroom/lounge lights in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
370
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
335
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
372

Similar threads

I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
938
There is one reason to have an inspection every three years instead of the five. It’s more work and money for them 😁😁
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top