On an installation there are two main switch’s one in a 12 way DB, another is an exel switch fuse supplying two DB’s. What would you put down as the main switch on the cert on page 2?
Thanks
 
i'd be doing a schedule of test results for each DB. then on each put the main switch details for each. on the inspection section, note saying "see DB schedules"
 
my bad. was looking at an old schedule where each had a main switch details for the DB.
 
If it has no isolator from DNO and the origin of supply is split then the most comprehensive way would be to complete 2 seperate certs.

It's no different to having a unrestricted and off peak supply at a house, some people do it on two certs and others just add a schedule of inspections and a schedule of tests, not right really but not a big deal in my eyes.
 

Reply to EICR certificate in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

That is what i am going to do. Thanks mate!
Replies
11
Views
691
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
455

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top