EICR code, commercial socket protection | on ElectriciansForums

Discuss EICR code, commercial socket protection in the UK Electrical Forum area at ElectriciansForums.net

W

Welchyboy

what code?

3036 fuses

Protecting double sockets in offices and workshop areas

not used for outside purposes ze/zs bonding etc fine!


C3?
 
Unless the installation is a special location such as Horticultural/Agricultural, then no code at all.
If the socket-outlets are for unsupervised general use by ordinary persons, then those socket-outlets will require RCD protection, not the circuit as a whole.
As such the code would be C3, and the observation would be perhaps: 'Lack of 30mA RCD protection to socket-outlets intended for unsupervised general use by ordinary persons, as per Regulation BS7671 411.3.3.'
 
Last edited by a moderator:
its a small glazing company, 1x dso staff in work shop making windows
3x dso owners office for it equiptment

i have coded a c3 - to current regs yes would require but retrospectivly no they wouldnt
 
its a small glazing company, 1x dso staff in work shop making windows
3x dso owners office for it equiptment

i have coded a c3 - to current regs yes would require but retrospectivly no they wouldnt
I'm assuming that you have issued a code C3 due to lack of RCD protection.
As yet, you haven't indicated any reason why the current Regs. would require RCD protection.
Socket-outlets only require RCD protection if they are used to supply mobile equipment outdoors, are in a special location or are intended for unsupervised general use by ordinary persons.
You've already indicated that there are no socket-outlets used to supply mobile equipment outdoors.
You've not mentioned a special location.
It's an office with a workshop, so I doubt that the socket-outlets are intended for unsupervised general use by ordinary persons.
Do they allow members of the public to wander in and start plugging in equipment?
 
Well my interpretation of 411.3.3 would be that an office worker or glass worker would be an ordinary person and the sockets would be for general use really, they would not be under supervision or instruction by any one with electrical knowledge or skill so yes a socket outlet under 20a would require it, I know people have different views on this reg and what is required but that's how I see it.

Under the definition section of the regs a skilled or instructed person is one with sufficient electrical knowledge to avoid danger, which I don't believe the above to definitely posses, so erring on the side of caution If it was a new install I would fit rcd protection to the sockets

Is this correct? I realise these people should be instructed/supervised in their general work activities, is this what is meant?

Some clarity on this situation would be grateful as it a bit unclear I think
 
Last edited by a moderator:
Regulation 16 of the EAWR: "No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger or, where appropriate, injury, unless he possesses such knowledge or experience, or is under such degree of supervision as may be appropriate having regard to the nature of the work."
The EAWR are a statutory requirement.
As such anyone using a socket-outket as part of their work duties would have to by law, meet the requirements to be considered skilled or instructed as per BS7671.
 
I would say that the equipment plugged into the sockets in a workshop is much more likely to be damaged than anywhere else, and as such would require RCD protection. I would certainly specify RCD sockets if a client insisted on 230v for a workshop.
 
What about cleaners, etc? And does skilled refer to skilled in their job, or does it include skilled in use of electrical outlets?

It is a bit of a double edged sword, do you risk the pain and suffering of coding as unsatisfactory, or risk the danger of comebacks in the perhaps unlikely event of a related incident?

I have debated the RCD point with Spin before, and it is not really black and white, but rather open to interpretation. I would go with the interpretation your support organisations adhere to.
 
Had it before, wanted to borrow a vacuum from the cleaner for a two minute job whilst she cleaned the bogs, apparently I'm not qualified!!!
 

Reply to EICR code, commercial socket protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

Understood, ; ) i'll pass it on to a company who do them day in day out i think.
Replies
8
Views
845
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top