Eicr code - db is dirty | on ElectriciansForums
Discuss Eicr code - db is dirty in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Tim
ESSEX
Hi guys,
Im doing an eicr on an events building, the db is in the main kitchen, however dirt and grime havegot into the db.
Would you code it?
Im thinking c3 as there is no sign of danger but improvements could be made. Or am i being too picky.
The cause of the grime getting in is the fact that the door hinge is broken, this has already been noted.
The pic is of the worst part[ElectriciansForums.net] Eicr code - db is dirty
Hope your all having fun on this winters day
Tim
A bit pedantic but, you could include this note in the original recommendation and record it all as one. i.e evidence of foreign bodies and grime within distribution board causing build up of dirt etc at MCB's within or something like that. C3. Check the MCB's for tightness etc and make sure all connections are secure.
If you have already noted the door missing I would probably note the grime issue with that, rather than a separate note. That way it falls in with the same code as the missing door.
Just wipe it down with a wet cloth........just kidding:wink5:
I'd just flag it up as a C3 on the same note as the door being broken
- - - Updated - - -
you beat me to it
A bit pedantic but, you could include this note in the original recommendation and record it all as one. i.e evidence of forgeign bodies and grime within distribution board causing build up of dirt etc at MCB's within or something like that. C3. Check the MCB's for tightness etc and make sure all connections are secure.
you beat us both to it!
Ill agree with the concensus that im being pedantic, ill include it in the code for the broken door hinge.
Cheers guys,
Tim
On a side note, look what i found above the sink. Code 1 i think. (I will fix this on site obviously)
And no dissing the voltage detector, they have their uses, however limited.
Make sure you make the relevant people aware about this C1 and ask if they would like for you to make it safe there and then. I agree they are handy. Its Voltage screwdriver phase testers whatever you want to call them that I hate.
May as well shake hands with your nearest 11kV Transformer.
I did check, and it was definatly live, i have now disconnected it from the dp isolator.
Volt sticks are good for indication, but i wouldnt bet my life on them
Cheers,
Tim
Reply to Eicr code - db is dirty in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net