Hi all new to form so thought I would as a question.
Testing a final ring circuit & all is normal apart from the live / brown legs of the circuit which are too short to reach the MCB so they have connected them together in a block & extended it within the CU via a 6mm to the MCB
Just wondering how you would code that if at all?
 

Attachments

  • [ElectriciansForums.net] EICR code for hybrid final ring cir
    20220201_102157.jpg
    690.3 KB · Views: 18
Ideally they should be extended separately with the same size cable as rest of circuit…
I might C3.
doesn’t have to be changed, but would save confusion when the schedule of test results says 2.5, but it’s 6mm leaving the breaker.
 

Reply to EICR code for hybrid final ring cir in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
Crimp or Wago inline connector, my preference would be Wago push fit...
Replies
1
Views
190

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top