If I am in a domestic situation and there are metal light switches I always check them, it will be 50/50 if they have a cpc to them.
 
All earth wires must be terminated to the back box.
An example that not all MF’s instructions are the be all and end all.
Pick shows the cpc from the cable not directly to the switch.
This does however highlight that a fly lead is required
 

Attachments

  • [ElectriciansForums.net] EICR Code for metal light switches with earth to backbox
    B849BD2C-110F-49CF-8288-BB01C7CFA772.png
    214.6 KB · Views: 22
Last edited:
the reasons i would give it a C3 is that it does not comply with MI ( as westie pointed out), and if the screws were removed for decorating or whatever, a fault on the switch would not trip MCB. therefore it "is improvement recommended. ", because i say so (smiley).
I’d be more concerned with the exposed conductive parts exposed by removing the switch personally.
 
All earth wires must be terminated to the back box.
An example that not all MF’s instructions are the be all and end all.
Pick shows the cpc from the cable not directly to the switch.
This does however highlight that a fly lead is required
It;s a M/C switch, terminate the cpcs into the back box and run a fly lead to the plate switch, how much would that cost you? not much I imagine then no need to code
 
My two pennyworth; I've always terminated cpc into back box, then a fly lead to faceplate. My thinking is if cpc become disconnected when plate is removed and/or replaced, is just that particular plate, not the rest of that circuit. I've even taken it further with multi gang switches, and put all cpc's in wago, then flylead to back box and plate, for the same reason, and also you can't successfully terminate multiple cpc's into one back box terminal.
 
the reasons i would give it a C3 is that it does not comply with MI ( as westie pointed out), and if the screws were removed for decorating or whatever, a fault on the switch would not trip MCB. therefore it "is improvement recommended. ", because i say so (smiley).
The MI instructions, in the case, are an illustration that the switch needs earthing not a prescription on how exactly to achieve this.

Jesus, the day I make my professional decisions based solely on what some monkey in the BG back office put together on his etch-a-sketch, I'll top myself.
 
C3 on the basis that it is earthed whilst screwed to the metal back box and should be 'safely isolated' before removing accessory, which by then cant be considered potentially dangerous as it is not live!
An improvement would then make it 'safer' for those s........d enough to remove it whilst 'live.!
 
All earth wires must be terminated to the back box.
An example that not all MF’s instructions are the be all and end all.
Pick shows the cpc from the cable not directly to the switch.
This does however highlight that a fly lead is required
Indeed. It also could be interpreted as suggesting that you need to sleeve the switchwire brown even if it's twin brown cable!
 
I guess it's just a case of doing what you think is safest...not "safe enough".
It costs a penny and 1 minute to run a fly lead from the plate to the back box, so if someone takes the front off and a fault occurs, there's a fine path to earth. Please don't drown me in tales of how you've got 500 a day to do and every second counts...lives matter (whatever hue) and if it's scorned as belt and braces and a piece of string too, so what? Let's not applaud a culture of doing what's just enough, but rather applaud a culture of doing everything we can to keep it safe. I'd much rather have 2 earths...
takes all the guesswork away, and who could criticise you for being extra careful?
We have all taken socket fronts off and found the conductors falling out of the back. Indeed, loose terminations are so common as to be de riguer in testing situations. Joe Bloggs trying to be neat with his decorating can easily fall foul of such problems as he tries to cut a neat paint-line in. Surely he shouldn't be expected to get an electrician in as he slaps some magnolia on his living-room walls?
 

Reply to EICR Code for metal light switches with earth to backbox in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
617
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
292

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top