I saw an eicr that gave a C2 for t&e cables that were in a chase with no capping/conduit, claiming 'no mechanical protection'. Wtf is the sheath dimlo ?!?!
Haha no. It was rough, chased out brickwork, no filling. But clipped.
Rough but fine basically
yeah well they probably had it in their minds that pvc/metal channels are `mechanical protection`...lol
this is typical Electrical Trainee stuff is this....i know caus i`v heard folk who i know are Electrical Trainee spouting it in the wholesalers...lol..
If the installation with no earthing conductor also contained a circuit with high protective conductor currents would that warrant a C1?
NO!
Read the definitions of C1 and C2 in the books.
It's written in plain English, 'Immediate' and 'Potentially'.
i did think this forum was grown up for a while. same old same old.
It still is, but you gotta admit, sometimes it is a good idea to run with the herd. Every book ever written on the new coding system would class no main earth as a C2, every electrician worth his salt would class it a C2, the regs class it a C2.... You see where this is going....
It is a C2, no argument. If you want to change the meanings to suit yourself then that's your prerogative, but it makes your reports worthless.
C1 means danger present, C2 means potentially dangerous. If the install is all tickedy boo except for a missing main earth, it is going to be perfectly safe at that moment in time isn't it! So a C2 it is.
NO!
Calm down dear, I was only asking a hypthothetical question.
I was only asking as if the installation contains circuits with high CPC currrents in normal use then without the main earth then there could potentially be a voltage relative to earth present at all metalwork connected to the CPC in question.
Obviously on discovering an installation with no main earth you would carry out some simple voltage tests to ascertain whether this has led to metal parts of the installation being at a voltage relative to metal objects connected to true earth which are available to touch.
I know its a C2 for no main earth, but if you have no main earth and identify a voltage between a metal DB and the exposed lead sheath of the incoming supply cable as a direct result of this then that could be immediately dangerous (I mean a real voltage not a ghost)
Haha...I'm always calm! :-)
Say there were raised voltages on Exposed parts, one might expect reports of people getting slight shocks.
Then, obviously, an Electrician would be called in to investigate. Still not an Immediate Danger though.
But in the general case, an install in good condition with a missing Earth, is potentially dangerous in the event of a Line to Exposed part fault, hence....C2.
You'd like to think so wouldn't you, but I went to a house a few months ago to do something or other and the lady mentioned that everyone felt a funny tingling when they touched a certain wall in the bathroom. I asked when this first happened and she said the day they moved in, which was about 13 years ago! (it was a cable in the wall with a capping nail touching live and after a shower the condensation made the wall damp enough to get a tingle)
There really is no helping those who can't help themselves
I would consider the lack of an earthing conductor to the MET to be immediately dangerous and hence a C1 (notwithstanding the fact that a fault would have to be present).
Can you get a shock from it all else being well with the installation?
No?
Then it's not immediately dangerous is it!!!
I can't knock you there because at the end of the day it's the inspector who decides what he thinks the code should be and he alone on his engineering assessment codes it, no-one else!. However all guidance on the matter to help the inspector decide points towards it being a C2 ....
You're right!
That's it! From now on, no 30mA RCD for additional protection gets a C1 from me!
You're right!
True to an extent but this is clear cut c2
The easiest way to define between c1 and c2 to is basically can this situation cause harm right now exactly how it is.
No earth can't, it just has the potential to under fault conditions
So C2
No?
I can't help playing devils advocate on this one.
Given the earth is functional as well as protective if the main earth is missing I'd say it would be reasonable to expect touch voltages of CPC to rise as electronic appliances are connected or even if there's an everyday surge or spike that causes surge arrestors to conduct. Neither of these events would be classed as faults so I could see the case for declaring it an immediate danger therefore I could see the case for declaring it a C1 issue.
Thats the beauty of an EICR, you as the inspector decides what you think the code should be based on your engineering assessment of the situation! If you live in a high 'surge' area, or have lots of electronics attached, or anything else that may introduce voltage onto the 'earth' then you may well declare it a C1 -- thats your engineering judgement!
If nothing of the sort exists then as a general rule C2 is recommended.
Nah!!! you both need to do your 14th edition to bring you in line.:tongue3:
well definately a bolt on then..
christ help the Electrical Trainee working to this when they cant even get their tiny minds round a main bond...
I think it 's not just 5WWs doing stuff like this - there are other factors. Firstly, as everyone knows , an eicr can bring in more work! There is still, and it's more prevalent in more technical trades, a (rightful!) distrust of sparks because people can make stuff up to get remedial work. Not sure how you can get round this one!!??
Secondly, there is a lot of hearsay - ppl taking stuff as read without thinking about it or looking at BGB. Eg - 12v light fittings/fans in bathrooms etc etc etc. I know I have been guilty of this but I am learning and am humble enough to be corrected.
But...solid education basis can definitely steer the 2nd kind of person - if it is drilled into them to question everything and how to use regs book well that helps too!
As for the cheating cowboys, I like to think that those blokes will never truly be successful and society and economics has a way of sorting wheat from chaff and honest from dishonest.
The only thing that can buck the trend is £millions spent on advertising, PR and marketing in the name of looking after people's world.
PREACH IT
EICR Code for no main earth
mamba,
Eddiesparks,