Esc do a good best practice guide. This is, i think, an example of a definite C2. Also waterpipe used as ME is a c2 too.
Induced voltages of up to 85?! Really?
Capacitively coupled phantom voltage maybe, but not induced.
Capacative coupling is the most common form of phantom voltages in conductors and they can be picked up using high impedance digital multimeters. A low impedance analogue multimeter will confirm the presence of a phantom voltage as they will not register a result.
is this some sort of homework?Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
dangerous under fault conditions.Yes C2 because C1 is for immediate dangers, where there is no earth it's only a C2 as its 'potentially dangerous'.
Esc do a good best practice guide. This is, i think, an example of a definite C2. Also waterpipe used as ME is a c2 too.
make notes as required....nothing more...nothing less..C2 and absolutely go to town on it in the Summary and Observations. If it were me, I think I'd do some sort of covering letter or note to the person ordering the report.
Yep ditto the above. Quite often find induced voltages of that size.. Nowhere to go without the main bond..!
what do you think the observations box is for Nick?C2 and absolutely go to town on it in the Summary and Observations. If it were me, I think I'd do some sort of covering letter or note to the person ordering the report.
wellYep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...
what do you think the observations box is for Nick?
That's why you go through the report with them and explain it to them isn't it?
ever heard of a danger notice Nick?Often they're wary and think you're just looking for work. A missing earth conductor I would want them to know I'm not messing. GN3 p.108 para.8 says an unrectified C1 should be notified urgently in writing; in the same vein I'd consider taking the personal decision to extend that to an extremely serious C2. Nothing says I can't, and it is difficult to prove a conversation took place. Something awful could easily happen with a missing earth conductor. It might be useful to be able to demonstrate later you took every reasonable step to draw their attention to the seriousness of the potential danger. Courts don't look favourably on important stuff buried in detail. I'm just risk averse; I can see why I'd do it. If you can't see why you'd do it, don't.