I've just completed an EICR and found a switch for towel rail in bathroom. It is located outside zones.
There is no RCD on this circuit, this is coded elsewhere.
My first thought was as located within 3M, Reg 701.512.3 code C2
But upon reading reg properly it specifically refers to sockets. I can't find anything for switches outside zones. So I can't see how to code, other than no code. But this then is same as light switch outside zones.
Any thoughts, I think I'm missing something, wet fingers on switches is never gonna end well?
There is no RCD on this circuit, this is coded elsewhere.
My first thought was as located within 3M, Reg 701.512.3 code C2
But upon reading reg properly it specifically refers to sockets. I can't find anything for switches outside zones. So I can't see how to code, other than no code. But this then is same as light switch outside zones.
Any thoughts, I think I'm missing something, wet fingers on switches is never gonna end well?