I was leaning towards a code 3 of improvement recommended given that the IR is fine and the set-up has been this way since 2007 i have been told. Maybe as others have suggested enhanced EICR frequency of 3-5 years. The property is a rental so has to be done every 5 years anyway.

As the question was raised, the cable feeds a 2 way CU in the garage which has its own RCD and then a lighting circuit and socket radial.
 
I was leaning towards a code 3 of improvement recommended given that the IR is fine and the set-up has been this way since 2007 i have been told. Maybe as others have suggested enhanced EICR frequency of 3-5 years. The property is a rental so has to be done every 5 years anyway.

As the question was raised, the cable feeds a 2 way CU in the garage which has its own RCD and then a lighting circuit and socket radial.
but what size is the T/E?
 

Reply to EICR code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
326
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
886
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
857

Similar threads

It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
828
That is what i am going to do. Thanks mate!
Replies
11
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top