Hate the EICR's at the moment...filling in one today on NIC software...section F,about 60 odd defects...then when you get to the tick box section you have to reference every one to defects in section F...constantly flicking back and trawling through all the defects....:cuss:
Regarding DI fittings, which are becoming more and more prevalent. I struggle between the two options of C2 and C3 mainly because. There is no danger present and there wont be if DA fittings remain, so for it to become dangerous there would need to be a change of fitting to class1 and however fitted it left the earths off, also a C2 tends to lead to an un-satisfactory condition. The problem with C3 is that its worded as a recommendation which i suppose is probably nearer to its actual real danger potential. As its relativly inexpensive to terminate them on a choc block and test continuity and there is some way to explain to the client that it is needed for the future then its easier to justify a C2. I do wish though that the suppliers of these lights create a term position for earth continuity would make life so much easier for DIYers and Electricians
the coding would be a code C3 as long as the lights are all class 2 and switches are all on plastic back boxes so plate screws cant become live. But I would make it clear on your test sheet or use addition sheet to clearly explain the dangers would increase if class 2 fittings were changed.
After all you can only report on the installation at its current state.
If you are in doubt ring NIC or ECA techinical (or whoever you pay your money to).
Reply to EICR codes again earths to double ins fittings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...