Hi all just carried out a eicr on a Chinese restraint. Below are what I found and the codes I would give any other suggestions would be appreciated. NO BONDING TO GAS OR WATER C2, NO SUPPLEMENTRY BONDING TO PIPEWORK NO RCD PRESCENT C2, NO EARTH ON METAL LIGHT FITTINGS C2, NO SLEEVINMG TO SWITCH LIVES C3, NO GROMMENTS TO BACK BOXES C3, NO RING FINAL CONTUNITY TO SOCKETS CIRCUIT ON A 32AMP MCB C2, JOINT BOX OUTSIDE STANDARD JB NOT IP RATED C2, LIGHTING CIRCUIT IN 1.0MM ON 16MCB C2, SOCKET SUPPLIED OFF LIGHTING CIRCUIT SUPPLYING A FRIDGE C2, SURFACE SOCKET BOX CRACKED ABLE TO GET FINGERS UP INSIDE BOX C1, NO EARTH SLEEVING C3, SOCKET SPURED FROM A SPUR ON 32AMP RING MAIN C2, NO GROMMET ON METAL GLAD SOCKET C3, TOILET LIGHTING OFF RING MAIN NO VISIABLE SIGN OF A SPUR IN CIRCUIT C2, PENDANT LIGHT FLEX MISSING OUTER SHEATH AT ENTRY TO FITTING C2. NO WARNING LABELS C3. Any suggestions would be great.