mcm

-
Joined
Oct 25, 2010
Messages
130
Reaction score
1
Hi all just carried out a eicr on a Chinese restraint. Below are what I found and the codes I would give any other suggestions would be appreciated. NO BONDING TO GAS OR WATER C2, NO SUPPLEMENTRY BONDING TO PIPEWORK NO RCD PRESCENT C2, NO EARTH ON METAL LIGHT FITTINGS C2, NO SLEEVINMG TO SWITCH LIVES C3, NO GROMMENTS TO BACK BOXES C3, NO RING FINAL CONTUNITY TO SOCKETS CIRCUIT ON A 32AMP MCB C2, JOINT BOX OUTSIDE STANDARD JB NOT IP RATED C2, LIGHTING CIRCUIT IN 1.0MM ON 16MCB C2, SOCKET SUPPLIED OFF LIGHTING CIRCUIT SUPPLYING A FRIDGE C2, SURFACE SOCKET BOX CRACKED ABLE TO GET FINGERS UP INSIDE BOX C1, NO EARTH SLEEVING C3, SOCKET SPURED FROM A SPUR ON 32AMP RING MAIN C2, NO GROMMET ON METAL GLAD SOCKET C3, TOILET LIGHTING OFF RING MAIN NO VISIABLE SIGN OF A SPUR IN CIRCUIT C2, PENDANT LIGHT FLEX MISSING OUTER SHEATH AT ENTRY TO FITTING C2. NO WARNING LABELS C3. Any suggestions would be great.
 
as OT saida C3 except if use outside is probable or special location electrics with no supp. bonding. and i'd C3 for the pendant flex.
 
Same as oldtimer said why C2, It's a 3
 
as OT saida C3 except if use outside is probable or special location electrics with no supp. bonding. and i'd C3 for the pendant flex.
All pipe work in the bathroom is not cross bonded and the no rcd protection to all circuits within the bathroom would you say this warrants a C2?
 
I saw am EICR on a job the other week, only done a few weeks ago.... The spark was still using code 4's

I have seen that, though the inspector had told me it was at the clients request as their maintenance systems in place were set up for the C1-C4 system.
Not sure on how this would fare in a court of law, as it obviously contravenes a NON statutory document.
 
'Grommets' - there is no requirement for them, so why say there is? If there is damage to the cable on entry to the box, then it is different, but you cannot say 'no grommets' without stating why, and what Reg.

Toilet light off RFC? Only a problem if the cable cannot carry the current, but if only one luminaire, then maybe 433.3.1 will apply anyway?
 

Reply to eicr codes anyone in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
620
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
308

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top